Since your submittal was approved and your argument has merit I would
agree but here is possible response.


"Standard weight pipe" or "standard weight" means a class of pipe weight
designated
by ANSI which is equivalent to schedule forty for nominal pipe sizes
ranging from
one-eighth of an inch to ten inches in diameter, and varies with pipe
dimension for
greater pipe diameters.

Top Myers
Myers Risk Services
961 Pottstown Pike
Chester Springs, PA 19425
[EMAIL PROTECTED] Web http://www.myersrisk.com
P- 610-321-2415 X219  C- 610-952-0965

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of rod
Sent: Saturday, November 18, 2006 3:16 PM
To: [email protected]
Subject: standard weight piping

I have a job where the piping specification for grooved pipe
reads " Grooved-End, Standard-Weight Steel Pipe: ASTM A
53/A 53M, ASTM A 135, or ASTM A 795, hot dipped galvanized
where indicated and with factory-or field formed,
square-cut-or roll-grooved ends."  We submitted, got
approval and installed ASTM A 135 schedule 10 piping. After
the fact the owner is questioning if we met the
specifications. The ME came back and said that although
there is nothing wrong with the piping that we installed,
our piping does NOT meet the specifications. I believe that
we do meet the specifications because the way I read it; we
had three choices. We chose ASTM A 135. I do not believe
that "standard weight" necessarily means schedule 40.
When looking at ASTM A 135 I do not even see a "standard
weight" designation. I guess I just think that if he
wanted schedule 40 he should have clearly stated it. I know
for a fact that if it didn't meet the specifications in
his mind; he should have rejected our submittals but that is
a mute point now. Am I out of line here or do I have a
legitimate argument? Did our pipe meet this specification?

 

Thank you for your input.

 

Rod DiBona

Rapid Fire Protection

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum