Burton,

Perhaps a local requirement ?.  We often hear references to national model
codes and standards such as NFPA. In actuality it's the adopted codes and
standards that count. Ask the AHJ to cite the adopted requirement, he or she
should be able to provide it. 

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Tuesday, November 21, 2006 5:19 PM
To: [email protected]
Subject: Re: Backflushing FDC's

It does NOT exist.  There was a proposal to add it to the 07  
edition.  IT was rejected if memory serves me right.

Roland

On Nov 9, 2006, at 8:36 AM, Ford, Charles wrote:

> In a local city, we are required to back flush FDC's every five  
> years. A discussion arose regarding
> NFPA 25 and back flush requirements. We have been unable to find  
> the requirement in 25. Anybody know
> where the requirement is?
>
>
> Burton Ford
>
> [EMAIL PROTECTED]
> 267-487-1000
> Fax 267-487-1010
>
> This e-mail transmission contains information that is intended to  
> be confidential and privileged.  If
> you receive this e-mail and you are not a named addressee you are  
> hereby notified that you are not
> authorized to read, print, retain, copy or disseminate this  
> communication without the consent of the
> sender and that doing so is prohibited and may be unlawful.  Please  
> reply to the message immediately
> by informing the sender that the message was misdirected.  After  
> replying, please delete and otherwise
> erase it and any attachments from your computer system.  Your  
> assistance in correcting this error is
> appreciated.  Thank you.  Cintas Corporation
>
>
>
>
>
> This e-mail transmission contains information that is intended to  
> be confidential and privileged.  If you receive this e-mail and you  
> are not a named addressee you are hereby notified that you are not  
> authorized to read, print, retain, copy or disseminate this  
> communication without the consent of the sender and that doing so  
> is prohibited and may be unlawful.  Please reply to the message  
> immediately by informing the sender that the message was  
> misdirected.  After replying, please delete and otherwise erase it  
> and any attachments from your computer system.  Your assistance in  
> correcting this error is appreciated.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to