how do you intend on notifying occupants in a office of a fire in the general warehouse, without an alarm? did you intend "smoke detection" instead of "fire alarm". The one pull-station rule is due to be (if not already) culled from the standard, but this also could shut-down the fan.
remember to include up to 2 sprinklers from under the obstruction in the hydraulic calc with the overhead. Scot Deal Excelsior Fire On 11/28/06, Scott A. Futrell <[EMAIL PROTECTED]> wrote:
Since fire alarm systems are not desired or required in most of these storage occupancies, the only fire alarm system that will shut down the fans is the operation of the water flow switch on the sprinkler systems and if that is delayed because of the fans, I fail to see how that helps the situation, or should be allowed. Scott (763) 425-1001 Office (612) 759-5556 Cell -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of hughes rewis Sent: Tuesday, November 28, 2006 7:14 AM To: [email protected] Subject: Big Ass Fans Well, I dug a little deeper into my filing system and found the documents sent to me from the manufacturer. In it ESFR sprinklers are discussed. In capsulated form it states that the two issues are obstruction and air velocity. First it says that the fans are shut down when the fire alarm system responds to a fire situation. Air velocity is typically limited to 5 ft/sec. It goes into great detail of test in several diffent senarios, of which I will not go into. Quite lenghty. Though I'd pass this along. Thanks, Hughes _________________________________________________________________ Stay up-to-date with your friends through the Windows Live Spaces friends list. http://clk.atdmt.com/MSN/go/msnnkwsp0070000001msn/direct/01/?href=http:/ /spaces.live.com/spacesapi.aspx?wx_action=create&wx_url=/friends.aspx&mk _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum