That is the entire system with the exception of a separate office area that
they have allowed us to exclude due to the separation and f=difference in
occupancy.
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, November 30, 2006 9:18 AM
To: [email protected]
Subject: Re: Overhead and Mezzanine calcs

the inclusion (or rather exclusion) of a mezzanine from a calculation  
of the ceiling is not my question.  IF including the additional 540  
sf below the mezzanine is causing a problem, it sounds like you are  
calc'ing just the 15X51.       What happened to the 3000 sf remote  
area or does this new room qualify for the room design?

Roland


On Nov 30, 2006, at 6:36 AM, Greg McGahan wrote:

>
> Normally we error on the side of caution but we have a situation  
> with calcs
> that are not working with more than a 2.4% cushion so I have to ask.
>
> Existing building with existing 3" water supply with new room and new
> mezzanine. The new room is 51' by 15' with a lower mezzanine that  
> is 36' x
> 15'. The remote area is specified at 3,000 sqft so there is no  
> reductions
> etc.
>
> Question:  Do I need to calculate the entire area with the mezz.? I  
> need
> something concrete to submit if I do not have to include them.
>
> Thanks,
> Greg McGahan
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to