We went ahead and included all of the heads and tweaked it until it squeaked to get a legitimate 10% safety factor. Thanks for the input.
Splitting hairs over 2-3 lbs is nuts in my opinion when the water supply can vary that much. Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Thursday, November 30, 2006 4:50 PM To: [email protected] Subject: Re: Overhead and Mezzanine calcs ah so. I interpreted existing building with a NEW room as having added an area to a facility that may have existing sprinklers adjacent to it. As for not adding a separate area that is a different occupancy - consider yourself lucky since that is not a basis for excluding it. We can have two different densities and spacing allowances within a single remote area. Roland On Nov 30, 2006, at 10:28 AM, Greg McGahan wrote: > That is the entire system with the exception of a separate office > area that > they have allowed us to exclude due to the separation and > f=difference in > occupancy. > Greg > > Living Water Fire Protection, LLC > 1160 McKenzie Road > Cantonment, FL 32533 > 850-937-1850 > Fax: 850-937-1852 > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Roland > Huggins > Sent: Thursday, November 30, 2006 9:18 AM > To: [email protected] > Subject: Re: Overhead and Mezzanine calcs > > the inclusion (or rather exclusion) of a mezzanine from a calculation > of the ceiling is not my question. IF including the additional 540 > sf below the mezzanine is causing a problem, it sounds like you are > calc'ing just the 15X51. What happened to the 3000 sf remote > area or does this new room qualify for the room design? > > Roland > > > On Nov 30, 2006, at 6:36 AM, Greg McGahan wrote: > >> >> Normally we error on the side of caution but we have a situation >> with calcs >> that are not working with more than a 2.4% cushion so I have to ask. >> >> Existing building with existing 3" water supply with new room and new >> mezzanine. The new room is 51' by 15' with a lower mezzanine that >> is 36' x >> 15'. The remote area is specified at 3,000 sqft so there is no >> reductions >> etc. >> >> Question: Do I need to calculate the entire area with the mezz.? I >> need >> something concrete to submit if I do not have to include them. >> >> Thanks, >> Greg McGahan >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum