We went ahead and included all of the heads and tweaked it until it squeaked
to get a legitimate 10% safety factor. Thanks for the input.

Splitting hairs over 2-3 lbs is nuts in my opinion when the water supply can
vary that much.

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, November 30, 2006 4:50 PM
To: [email protected]
Subject: Re: Overhead and Mezzanine calcs

ah so.  I interpreted existing building with a NEW room as having  
added an area to a facility that may have  existing sprinklers  
adjacent to it.

As for not adding a separate area that is a different occupancy -  
consider yourself lucky since that is not a basis for excluding it.   
We can have two different densities and spacing allowances within a  
single remote area.

Roland

On Nov 30, 2006, at 10:28 AM, Greg McGahan wrote:

> That is the entire system with the exception of a separate office  
> area that
> they have allowed us to exclude due to the separation and  
> f=difference in
> occupancy.
> Greg
>
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Roland
> Huggins
> Sent: Thursday, November 30, 2006 9:18 AM
> To: [email protected]
> Subject: Re: Overhead and Mezzanine calcs
>
> the inclusion (or rather exclusion) of a mezzanine from a calculation
> of the ceiling is not my question.  IF including the additional 540
> sf below the mezzanine is causing a problem, it sounds like you are
> calc'ing just the 15X51.       What happened to the 3000 sf remote
> area or does this new room qualify for the room design?
>
> Roland
>
>
> On Nov 30, 2006, at 6:36 AM, Greg McGahan wrote:
>
>>
>> Normally we error on the side of caution but we have a situation
>> with calcs
>> that are not working with more than a 2.4% cushion so I have to ask.
>>
>> Existing building with existing 3" water supply with new room and new
>> mezzanine. The new room is 51' by 15' with a lower mezzanine that
>> is 36' x
>> 15'. The remote area is specified at 3,000 sqft so there is no
>> reductions
>> etc.
>>
>> Question:  Do I need to calculate the entire area with the mezz.? I
>> need
>> something concrete to submit if I do not have to include them.
>>
>> Thanks,
>> Greg McGahan
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to