I was told unofficially that this was probably an oversight in the original
text and the intent was probably the same as the exception in 13. I was
advised to meet with the local AHJ and make the argument to him and try to
get his blessing.
Hope this helps.
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Gouveia
Sent: Friday, December 01, 2006 9:39 AM
To: [email protected]
Subject: Re: NFPA 409

Greg,
I just recieved a similar job and was wondering if you found any further
clarification on the max 12'-0" spacing for NFPA #409 sprinkler system.  So
far I have been unable to find the background for this requirement.

Thanks,
Mark Gouveia
Sprink Tech





On 11/13/06, Greg McGahan <[EMAIL PROTECTED]> wrote:
>
> NFPA #409 states the following:
>
> 7.2.3 Sprinkler spacing shall be as specified in 6.2.2.3.
>
> 6.2.2.3 In aircraft storage and servicing areas, the protection area as
> projected on the floor shall be limited to 12 m2 (130 ft2). The maximum
> distance between sprinklers either on branch lines or between branch lines
> shall be 3.7 m (12 ft).
>
>
> There is no exception like in NFPA #13 that allows spacing of 12'-6" in
> bays
> 25' wide that I can find.
>
> Is this as absolute as it sound, or is there something I am missing? This
> kills a reasonable layout due to the dimensions of this building.
>
> Thanks,
> Greg
>
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to