Chris:

I'm don't agree with the, "... requirements for gpm and pressure are broke 
beyond repair ..." smack, but I'm with you on, "... FD's haven't a clue what 
they want or need ..."    I made a proposal in committee that we add a 
provision for hydraulic analysis of the actual hose nozzle set-up used by the 
serving fire department in determining the required outlet pressure, to 
essentially performance-engineer Class 1 standpipes, but it was voted down as 
too cumbersome.    

Here's the challenge:  As Chris says, it's foreseeable that certain hose nozzle 
set-ups can require much higher outlet pressure to deliver the required 
residual at the tip.  If the standard rig is a 2-1/2" gated wye with two 1-1/2" 
x 100' hoses the required outlet pressure to deliver 100 at the tips is almost 
150 PSI.   But not all nozzles are rated for 100 PSI - that just happened to be 
the first performance point at which a couple of manufacturers tested and 
received listings for their nozzles.

Using Task Force Tips as an example, they now offer nozzles that are designed 
for as low as 45 PSI up to 100 PSI; I think they have 45, 75 and 100 PSI model 
families.   The 45's and 75's work great with lower residuals at the tip and 
bring the required outlet pressure to or near 100.   (Let's keep in mind that 
the nozzles are functional at lower pressures than their ratings, but may not 
meet the patterns and performance of their listings.)  But it's really up to 
the serving FD to tell the designer what they need, based on the equipment 
their firefighters carry into buildings, and that should drive the design 
criteria.

Here in San Diego, the FD specified a new high-rise pack with a 75 PSI nozzle - 
they're updating all of their trucks.   New policy in this city, based purely 
on performance criteria, is 115-120 PSI at discharge; regardless of the 
specifics of nozzle performance or actual residual at the tip, this is what the 
FD wants based on full flow exercises they ran at their training facility.   
That's the way it should be - and that's how we can continue to shape NFPA 14 
to "fix" it in this regard.   But any chain of events is only as strong as its 
weakest link, and in this case it's the interaction between industry and fire 
service to query the serving departments about how they want standpipe systems 
to perform.   Be proactive about asking and make them tell you ...


Steve Leyton
Protection Design & Consulting


The foregoing is the opinion of the writer alone, and does not necessarily 
represent the intent of the NFPA 14 Technical Committee, nor constitute a 
formal or informal interpretation of the standard.




-----Original Message-----
From: Chris Cahill [mailto:[EMAIL PROTECTED]
Sent: Wednesday, December 06, 2006 8:44 AM
To: [email protected]
Subject: RE: pump capacity/standpipe


If you review what the FD actually uses you will probably find it's much
higher than 100psi.  A popular set up is 100 psi nozzles with 1-3/4" hose
200' which is 132 psi at the outlet at 100 gpm.  Then there is no guessing
what they will be using 5 years from now.  Through the 80's and 90's
required average pressures went up as a general trend.  They seem to be
going down IMHO in the '00's.  Trends are irrelevant though when speaking of
a particular job in a particular city. 

NFPA 14 requirements for gpm and pressure are broke beyond repair and FD's
haven't a clue what they want or need, thus why NFPA 14 is broke.  If I knew
how to fix it I would send in a proposal, but I don't.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Wednesday, December 06, 2006 10:14 AM
To: [email protected]
Subject: Re: pump capacity/standpipe

I don't want to beat this horse to death like a "Big Ass Fan", but it would 
be prudent if you reviewed the changes to 14 for 2007, and reviewed the 
equipment used by the AHJ, to meet the hose and Nozzle friction loss calc's.

(They may actually be lower than the 100 Psi at the outlet depending on the 
nozzle.)

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Joe Hankins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, December 06, 2006 8:49 AM
Subject: Re: pump capacity



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to