The joists are non-combustible. The entire assembly is non-combustible. Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Tuesday, December 12, 2006 8:49 AM To: [email protected] Subject: RE: Outside Restaurant Seating The reference to noncombustible and limited combustible construction applies to the entire canopy assembly and not just the exposed surface. Based on what you described, I believe sprinklers are required below and possible inside the canopy depending on the type of wood joists. I would look at the new 2007 of NFPA 13 because it has changed with regard to canopies. Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Michael O'Brian Sent: Monday, December 11, 2006 6:26 PM To: [email protected] Subject: RE: Outside Restaurant Seating I agree with Kurt look at the new appendix item (new in 2002 so I guess its old now) A.8.14.7.1 Balconies, decks, and similar projections from the building should be treated as exterior roofs and canopies when applying the criteria of 8.14.7.1. So if it meets the requirements found in 8.14 then it famous code words it depends. I am not sure if the stucco would meet the non-combustible requirements found 8.14.7.2 Michael O'Brian Code Savvy Consultants www.codesavvyconsultants.com 313-618-6401 Fax 313-557-0294 ************************************************ Coming soon www.inspector911.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Monday, December 11, 2006 12:17 PM To: [email protected] Subject: Outside Restaurant Seating We are looking at a large (1,300 sqft) noncombustible balcony that is going to be used as restaurant seating as part of a Country Club. Previously we bid this as protected because the balconies had exposed combustible ceilings. Since they have revised this to stucco noncombustible finishes I am not sure how to look at it. Thanks for your help, Greg McGahan _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum