The joists are non-combustible. The entire assembly is non-combustible.

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Tuesday, December 12, 2006 8:49 AM
To: [email protected]
Subject: RE: Outside Restaurant Seating

The reference to noncombustible and limited combustible construction applies
to the entire canopy assembly and not just the exposed surface. Based on
what you described, I believe sprinklers are required below and possible
inside the canopy depending on the type of wood joists. I would look at the
new 2007 of NFPA 13 because it has changed with regard to canopies.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Michael
O'Brian
Sent: Monday, December 11, 2006 6:26 PM
To: [email protected]
Subject: RE: Outside Restaurant Seating

I agree with Kurt look at the new appendix item (new in 2002 so I guess its
old now)

A.8.14.7.1 Balconies, decks, and similar projections from the building
should be treated as exterior roofs and canopies when applying the criteria
of  8.14.7.1.  

So if it meets the requirements found in 8.14 then it famous code words it
depends.  I am not sure if the stucco would meet the non-combustible
requirements found 8.14.7.2

Michael O'Brian
Code Savvy Consultants
www.codesavvyconsultants.com
313-618-6401
Fax 313-557-0294
 
************************************************
Coming soon www.inspector911.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Monday, December 11, 2006 12:17 PM
To: [email protected]
Subject: Outside Restaurant Seating

We are looking at a large (1,300 sqft) noncombustible balcony that is going
to be used as restaurant seating as part of a Country Club.

Previously we bid this as protected because the balconies had exposed
combustible ceilings. Since they have revised this to stucco noncombustible
finishes I am not sure how to look at it.

Thanks for your help,
Greg McGahan


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to