What temperature will the K8.0 TY-FRB heads be?  Only the 135 degree
heads are listed for QR at 16x22.  So it should be okay to use 155
degree heads.

Thanks,
 
Trever Williams
Designer
Unlimited Sprinkler Fire Protection
11130 Petal St.  Suite 800
Dallas, TX  75238
214-349-8444 - Phone
214-349-8450 - Fax
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
Sent: Friday, December 15, 2006 5:02 PM
To: [email protected]
Subject: both QR & SR sprinklers

I have been looking at an existing hotel building where each guest room
has
a Central GB-LO extended coverage sidewall sprinkler covering the
sleeping
area and a Central Model H sidewall covering the space between the
sleeping
are and the room door. Since the GB-LO's are under recall, they are
going to
be replaced, most likely with Tyco TY-FRB K8.0 extended coverage
sidewalls.
My question is this; the Model H is a standard response sprinkler and
the
TY-FRB's are listed for both standard and quick response. Even though it
is
listed for SR, I assume that the response time is in QR territory. Is
there
going to be a problem mixing these two sprinklers? The demand area is
the
two sprinklers and the FRB spacing is 16x22 and we are using UL
criteria.

 

 

Todd G. Williams, PE

Fire Protection Design/Consulting

Stonington, Connecticut

860.535.2080

www.fpdc.com

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to