"The fire is going to activate any head" is a poor argument when considering
the listing requirements of SR vs QR in the plunge test. The "plunge test"
is an oven that has hot air circulating through it.  The sprinkler is placed
in a panel of the oven and "plunged" into the hot air.
 
The QR sprinkler must activate in 14 seconds.  The SR sprinkler has an
astounding 100 seconds to activate when you do this test.  These are UL
requirements and FM varies a bit.  It is amazing how much the mass of the
element matters here.   But if you can't see an improved life safety factor
when sprinklers will activate that much sooner, there is no use continuing
the discussion.

As for me and my house, we have QR and residential heads installed to
protect us while visions of sugarplums dance in our heads. Fortunately we
had the opportunity to upgrade since one of our suppliers offers us the
evolving continuum of new technology as it becomes available :)

Have a firesafe and enjoyable Holiday, all ! 

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Thursday, December 21, 2006 12:10 PM
To: [email protected]
Subject: Re: both QR & SR sprinklers

Craig:

Take in a Residential fire Demo Trailer next chance you get! Volunteer to be

inside, you'll then know what we're talking about.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, December 21, 2006 9:28 AM
Subject: RE: both QR & SR sprinklers


Chris, I'll take your word for it.  (Although I'm a bit disturbed at you
and Matt's repeated setting of things on fire.)  LOL


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to