If the rest of the system is a 13R system would the floor joist construction
also qualify as a 13R?

Karen Purvis
Designer
Facility Systems Consultants
Knoxville, TN 37902
865-246-0164

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Friday, December 22, 2006 11:12 AM
To: [email protected]
Subject: RE: Floor Joist question

Karen:

There is a lot of information needed in order to help you, but I can't
think of any 1'-9" deep floor joist construction what wouldn't require
sprinklers with the following exceptions:

1. qualifies for a NFPA 13R design
2. space is filled entirely with noncombustible insulation.

8.14.1.2.1 relates to noncombustible or limited combustible
construction, which typically does not include wood floor joists.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 