Mark:
I'm with you on this, but only as a minimum, and NO WAY on OH-I! Closely
racked plastic carts more closely resemble a 4-5' high pile of plastic
pallets, than any other commodity. If you look at the Hose demand for Group
A plastics less than 5' in Table 12.2.1.2 your looking at a 500 Gpm demand,
obviously not the low end of OH which is 250 Gpm, and a lot closer to EH.
What would you do with a 40x40 area full of plastic pallets 5' high.
That's the direction I would follow.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Mark Sornsin" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, December 22, 2006 7:16 AM
Subject: RE: Grocery Store Cart Storage...
OH, Gr. II sounds reasonable for storage of plastic carts at a grocery
store.
Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
701.280.8591
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Haugen,
Charles
Sent: Thursday, December 21, 2006 4:13 PM
To: [email protected]
Subject: RE: Grocery Store Cart Storage...
Plastic Carts...
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Haugen,
Charles
Sent: Thursday, December 21, 2006 12:03 PM
To: [email protected]
Subject: RE: Grocery Store Cart Storage...
I have a call into the G.C....
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Thursday, December 21, 2006 11:59 AM
To: [email protected]
Subject: RE: Grocery Store Cart Storage...
Are the carts made of plastic like so many that I have seen recently?
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Haugen,
Charles
Sent: Thursday, December 21, 2006 12:54 PM
To: [email protected]
Subject: Grocery Store Cart Storage...
Question:
Grocery Store 'Cart Storage' area - considered .15 / or .20 Density?
Granted - nothing combustible in this room unless like other grocery
stores... they have displays, etc... in this area as well... (The word
'Storage' is the reason I'm asking the question.)
Any comments? Thanks in advance!!
Charles Haugen
SimplexGrinnell - Fargo, ND
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
************************************************************************
**********************
IMPORTANT: The contents of this email and any attachments are
confidential. They are intended for the named recipient(s) only.
If you have received this email in error, please notify the system
manager or the sender immediately and do not disclose the contents to
anyone or make copies thereof.
************************************************************************
**********************
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum