The demand calc for this system may have a safety factor. It might be worth 
doing a supply calc to see what the actual flow/pressure/density would be with 
all the design area heads open. It could be that the actual density is high 
enough (though not likely with an original OH2 design), depending on how good 
the supply is. From a customer service standpoint, you could show the owner 
that at least you are looking at all options. 
   
  Just my thoughts,
   
  J. Scott Mitchell, P.E.

Todd Williams <[EMAIL PROTECTED]> wrote:
  I am working on a project where the owner is going to store a Class 3
commodity in cardboard boxes and a Group A Plastic in cardboard boxes. These
are to be stored on pallets in racks. Based on the available density, the
Class 3 can be stored to 12 feet and the plastic to 5 ft. The owner wants to
store the plastic on the first level and the Class 3 on the second level,
immediately over the plastic. His argument is that it meets both criteria,
but I am suspect that the total fire load of a class 3 on top of plastic
might be greater than the system (currently designed for OH2) can handle.
However, I don't see anything that backs me up. I want him to dedicate
separate racks for each. Any thoughts?



Todd G. Williams, PE

Fire Protection Design/Consulting

Stonington, Connecticut

860.535.2080

www.fpdc.com