This isn't in the national codes but local or state jurisdictions may
have code modifications that allow that.

Eric J. Shelton, PE
Senior Fire Protection Engineer

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060 

v: (804) 285.4171 f: (804) 217.8520
http://www.haengineers.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ken
Holsopple
Sent: Tuesday, January 09, 2007 10:52 AM
To: [email protected]
Subject: RE: hydraulic elevators

>Greg wrote:

> No head in the elevator equipment room either as it is dedicated for
that
equipment.


Greg,
 What was the basis for omitting the sprinklers in the elevator
equipment
room? Would this be based on the exemptions provided by the IBC? If the
elevators are the hydraulic type, then combustibles are present.

Ken Holsopple
Rowe Sprinkler Systems, Inc.