Agreed.  For the sprinkler to activate, the ceiling needs to be there for both 
fuel sources:  debris or hydraulic fluid.

John, now as to your contention that most times the car rests at the terminal 
floor, I guess your luck with elevators is better than mine.  Seems whenever I 
go into to a multi-story building, the elevators are all near the top of the 
building!!

I would still love to hear from contractors as to how many of those sidewalls 
they have changed due to a fire in the pit.  And, George, I know about that 
form in the back of the book, so if I get the data I will submit the proposal 
to 13.

--
David de Vries, P.E., CSP 
Firetech Engineering Incorporated 
[EMAIL PROTECTED]

-------------- Original message -------------- 
From: "John Drucker" <[EMAIL PROTECTED]> 

> David, 
> 
> The same "no ceiling" situation would hold true for fires involving 
> combustible hydraulic fluids. But consider that most times an elevator car 
> "rests" at the terminal floor at or a floor above the pit creating the 
> requisite thermal barrier. 
> 
> John Drucker 
> Fire Protection Subcode Official 
> New Jersey 
> 
> 
> 
> -----Original Message----- 
> From: [EMAIL PROTECTED] 
> [mailto:[EMAIL PROTECTED] On Behalf Of David de 
> Vries/Firetech 
> Sent: Wednesday, January 10, 2007 3:06 PM 
> To: [email protected] 
> Subject: RE: hydraulic elevators 
> 
> Bill: 
> 
> You raise a good point -- what is the fire loss experience in elevator 
> shafts? 
> 
> Do we have a history of such fires? (Probably do, with debris then cigarets 
> dropped down the gap between the cab and the floor.) 
> How often does a sidewall sprinkler activate when there is such a fire? 
> Was the elevator cab at its lowest position such that heat from the fire 
> could activate the sprinkler? (If we have no "ceiling" to direct the heat 
> to the sprinkler, unless the fire is directly below the sprinkler, it will 
> probably not activate.) 
> 
> If no contractor on this forum has ever been called out to restore a system 
> (change out the one sidewall sprinkler) after a fire in the pit of an 
> elevator, hydraulic or traction, then the 13 committee needs to know. Maybe 
> we can do without one there. 
> 
> -- 
> David de Vries, P.E., CSP 
> Firetech Engineering Incorporated 
> [EMAIL PROTECTED] 
> 
> -------------- Original message -------------- 
> From: "Brooks, Bill" 
> 
> > Nothing the committee does is contradictory (by definition)! It only 
> > appears contradictory until there is an explanation that makes the 
> apparent 
> > contradiction plausible. 
> > 
> > So... 
> > 
> > It appears the committee is saying: 
> > 
> > 1. Debris - combustible fluid = no hazard 
> > 2. Debris + combustible fluid = hazard 
> > 
> > By itself, any quantity of accumulated debris is not a hazard. Wouldn't 
> > this be borne out by past experience? Does this remove the contradiction? 
> > 
> > Bill Brooks 
> > Pittsburgh, PA 
> > 
> > -----Original Message----- 
> > From: [EMAIL PROTECTED] 
> > [mailto:[EMAIL PROTECTED] Behalf Of John 
> > Drucker 
> > Sent: Monday, January 08, 2007 1:42 PM 
> > To: [email protected] 
> > Subject: RE: hydraulic elevators 
> > 
> > 
> > The NFPA-13 hoistway pit suppression requirement is contradictory. The 
> > explanatory material states; " The sprinklers in the pit are intended to 
> > protect against fires caused by debris, which can accumulate over time." 
> > The exception permits the omission of sprinklers in hoistway pits that 
> > are enclosed, of non combustible construction and that do not contain 
> > combustible hydraulic fluids. So what happened to the debris ?. The 
> > removal of combustible hydraulic fluids does not alleviate the debris 
> > issue. A hazard still exists. 
> > 
> > Additionally the non combustible fluid issue is not addressing hydraulic 
> > elevators but rather traction elevators that don't utilize hydraulics as 
> > their means of locomotion. 
> > 
> > John Drucker 
> > Fire Protection Subcode Official 
> > New Jersey 
> > 
> > 
> > -----Original Message----- 
> > From: [EMAIL PROTECTED] 
> > [mailto:[EMAIL PROTECTED] On Behalf Of Roland 
> > Huggins 
> > Sent: Monday, January 08, 2007 1:17 PM 
> > To: [email protected] 
> > Subject: Re: hydraulic elevators 
> > 
> > the problem with hydraulic oil is not how well it burns in standard 
> > liquid form (ie flash point). It's when a small leak occurs under 
> > pressure and you get atomized oil spraying out. As a comparison, 
> > grain dust laying on the ground is not that big a deal but when 
> > floating in the air, can go boom. 
> > 
> > Roland 
> > 
> > On Jan 8, 2007, at 9:57 AM, Loren Johnson wrote: 
> > 
> > > In my dealings with FM Global, their Approval Guide 
> > > does list manufacturers who have a less hazardous type 
> > > of hydraulic fluid, which has a higher flash point 
> > > than normal hydraulic fluids. FM indicates that these 
> > > too will burn under certain conditions, but the fire 
> > > risk has been reduced to an acceptable degree. 
> > > 
> > > Loren Johnson - CFPS, CET 
> > > Fire Protection Systems Consultant 
> > > The Hitchcock Company 
> > > Peoria, IL 
> > > --- [EMAIL PROTECTED] wrote: 
> > > 
> > >> I had been told by one elevator inspector that there 
> > >> was an FM approved 
> > >> hydraulic media that was non-combustible and if that 
> > >> was being used the 
> > >> sprinkler in the pit could be deleted. 
> > >> 
> > >> On the other hand in another jurisdiction I was told 
> > >> that regardless of 
> > >> the hydraulic media used that we were to provide a 
> > >> sprinkler in the pit 
> > >> due to the possible accumulation of miscellaneous 
> > >> debris which could 
> > >> catch fire. 
> > >> 
> > >> 
> > >> Isn't it wonderful to be in an industry where 
> > >> everything is so black and 
> > >> white? ;) 
> > >> 
> > >> 
> > >> 
> > >> Craig L. Prahl, CET 
> > >> Fire Protection Group 
> > >> Mechanical Department 
> > >> CH2MHILL 
> > >> Lockwood Greene 
> > >> 1500 International Drive 
> > >> PO Box 491, Spartanburg, SC 29304-0491 
> > >> Direct - 864.599.4102 
> > >> Fax - 864.599.8439 
> > >> [EMAIL PROTECTED] 
> > >> http://www.lg.com 
> > >> 
> > >> 
> > >> -----Original Message----- 
> > >> From: [EMAIL PROTECTED] 
> > >> [mailto:[EMAIL PROTECTED] On 
> > >> Behalf Of George 
> > >> Church 
> > >> Sent: Monday, January 08, 2007 10:41 AM 
> > >> To: [email protected] 
> > >> Subject: RE: hydraulic elevators 
> > >> 
> > >> Perhaps everyone else in the area installs to #13R ? 
> > >> Perhaps a call to the local AHJ(s) would clear up 
> > >> whether you're the 
> > >> only one doing it correctly, in which case maybe 
> > >> your competitors will 
> > >> be a little dismayed to find themselves going back 
> > >> and retrofitting 
> > >> their bottoms. The call to the AHJ(s) could be 
> > >> two-fold: ask them if 
> > >> they believe it should be required; and ask WHY it 
> > >> is not- you may find 
> > >> in the near future you're no longer alone in the 
> > >> shaft. 
> > >> 
> > >> George Church 
> > >> Rowe Sprinkler 
> > >> 
> > >> -----Original Message----- 
> > >> From: [EMAIL PROTECTED] 
> > >> [mailto:[EMAIL PROTECTED] On 
> > >> Behalf Of David de 
> > >> Vries/Firetech 
> > >> Sent: Monday, January 08, 2007 10:30 AM 
> > >> To: [email protected] 
> > >> Subject: Re: hydraulic elevators 
> > >> 
> > >> Pat on the back to the only contractor in the area 
> > >> complying with this 
> > >> provision of 13. 
> > >> 
> > >> -- 
> > >> David de Vries, P.E., CSP 
> > >> [EMAIL PROTECTED] 
> > >> 
> > >> -------------- Original message -------------- 
> > >> From: "Greg McGahan" 
> > >> 
> > >>> 
> > >>> We are receiving mixed reviews from AHJ's 
> > >> regarding this issue: Are 
> > >>> sprinklers required in the bottom of hydraulic 
> > >> elevator shafts? 
> > >>> 
> > >>> I know what the code says but we have never been 
> > >> able to document that 
> > >> 
> > >>> ANY 
> > >> 
> > >>> hydraulic elev fluid is non-combustible by 
> > >> definition. I was informed 
> > >>> this 
> > >> 
> > >>> morning that we are the only contractor in the 
> > >> area putting sprinklers 
> > >> 
> > >>> in the bottom of these shafts. 
> > >>> 
> > >>> Thanks, 
> > >>> Greg McGahan 
> > >>> 
> > >>> 
> > >>> 
> > >> 
> > >> _______________________________________________ 
> > >> Sprinklerforum mailing list 
> > >> [email protected] 
> > >> 
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > >> _______________________________________________ 
> > >> Sprinklerforum mailing list 
> > >> [email protected] 
> > >> 
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > >> 
> > > 
> > > 
> > > __________________________________________________ 
> > > Do You Yahoo!? 
> > > Tired of spam? Yahoo! Mail has the best spam protection around 
> > > http://mail.yahoo.com 
> > > _______________________________________________ 
> > > Sprinklerforum mailing list 
> > > [email protected] 
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > > 
> > 
> > _______________________________________________ 
> > Sprinklerforum mailing list 
> > [email protected] 
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > 
> > 
> > 
> > _______________________________________________ 
> > Sprinklerforum mailing list 
> > [email protected] 
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > _______________________________________________ 
> > Sprinklerforum mailing list 
> > [email protected] 
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to