And if you dig around the archives at AFSA virtually (or buy Roland lunch)
you'll find a dissertation on why the velocity shouldn't be limited- it's
because when you are whizzing that much water the friction loss, as Thom
pointed out, is so excessive that the loss quickly adds up and you run outa
water supply. UNLESS you have a heckuva water supply (again, as Thom
normally has unless water delivery is via high velocity avalanche) in which
case there's no reason you cannot have high velocities....except that if the
fire doesn't grow in the shape we assume it will, or for some other reason
one extra head opens on a branch line that you didn't figure on, and the
delivered density goes kaput.

FM was 20 fps, thought they might still have the "acme grinnell rule" for
lines less than 2" in diameter. Anytime I get flack about velocity, I sic
Roland on em. I'm surprised he didn't jump back on this favorite soapbox of
his.

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, January 09, 2007 6:49 PM
To: [email protected]
Subject: Re: max velocity

Because we use Hazen Williams for fire sprinkler design, this formula 
already creates a pressure penalty for excessive velocity, therefore no 
limit is put on fire sprinkler system velocities.

Just as a side note Backflow preventors are tested and usually listed at 10 
Fps, if your exceeding the flow limits of the backflow preventor you can 
damage it in full forward flow testing.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Ivan Cabrera" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, January 09, 2007 3:57 PM
Subject: max velocity


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to