Roland,
If I understand you correctly, in my particular situation, I have a
school of light hazard occupancy with a small mechanical room in the
basement (walls all around).  I need to size a tank for this project so
I could size the water supply for a 30 minute duration instead of the 60
minute  required for OH?
Thanks,
Dewayne  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, January 11, 2007 2:04 PM
To: [email protected]
Subject: Re: water supply duration

It depends if the 800 sf is separated by a wall (not rated but just a
wall).  If it is, the size of your remote area is based on the lower  
overall building occupancy.   If no wall, then the size is based on  
the higher hazard occupancy.   See 13:A.;11.2.3.2.1.1.    Your hose  
demand, though not stated in the Annex example, is understood to be
directly tied to that.

Roland


On Jan 10, 2007, at 1:30 PM, Dewayne Martinez wrote:

> What would the appropriate water supply duration be for a building 
> overall light hazard occupancy but with a storage room of 
> approximately 800 sq ft in it.  I need to size a water storage tank 
> and 30 vs..
> 60 min
> makes a difference.  I saw the hose demand exception in NFPA for rooms

> less than 400 sq ft. but this did not address the duration.  I tried 
> to access the archives but they seem to be down.  Any help and 
> possibly a NFPA reference # would be appreciated.
> Thanks
> Dewayne
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to