Hmmm. More to the point brought up that inspections of improperly
installed
(or designed) systems are now null and void.
Well, I don't know your confidence level, but from what I've seen, we are
NOT a perfect industry. Day in and day out, gray areas and fitter
mistakes,
design mistakes, fab errors, wrong heads show up and get installed, duct
changes, architectural changes- all these combine so I can about guarantee
you that virtually NO systems installed are "perfect". I don't expect any
argument from anyone on this. Therefore, the systems we install are not
compliant with NFPA #13- if you were to take a fine-tooth comb and go thru
EVERYTHING. I'm not saying, and out industry's amazingly great track
record
doesn't argue, that the systems aren't good, aren't workable, and aren't
REASONABLY compliant.
BUT
Any of us who have been involved in lawsuits will agree that all common
sense and what is "generally accepted" can quickly go out the window in a
court of law and the most inane arguments can win. I had a competitor's
lawyer argue
a) that I wasn't competent to testify on the subject of inspections and
whether a system was compliant and
b) that NFPA #13 was NOT part of the city's fire code.
Understand the system we're talking about was installed to protect a
grocery
store, was designed to light hazard occupancy (by a Level IV) using the
largest room rule (ignoring the sales floor since the largest room was
"remote"- and wasn't even a room, it was a ceiling elevation change. The
system demand was 66 GPM plus 100 GPM hose allowance, the "backflow" was a
pair of plumber's brass swing cheks (2") between 1/4 turn ball valves,
with
a 1.5" residential FDC. Did I mention the combo ITC/main drain was a 3/4"
boiler drain stuck in a FIT tee above the "BFP" ? My dog is competent to
tell you this system is non-compliant. And this was a different one than
the
CPVC system installed by same guy, guess he's just not very good at
mercantile. Ironically, he complains how others violate the code!
So when we go inspect a system, or deeper, perform a full gamut of ITM
(and
there's an interesting dilemma- quote ITM when your competitor quotes I
and
you will be high bidder) - and since it's noncompliant, I'm outside NFPA
#25
when the place burns down.
AARRRGHHHHHHHHHHHH how do we owners sleep at night?
George Church
Rowe Sprinkler
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, January 11, 2007 12:14 PM
To: [email protected]
Subject: RE: Testing
John, I believe what you said has merit to a point. I believe that
every inspection should entail more than just ringing the bell.
Unfortunately that's all a lot of owners want to pay for and that what a
lot of inspectors do. It's a fast easy way to make a buck.
The inspection should point out any obvious visible deficiencies but to
what degree would or could and engineer perform any kind of absolutely
certifiable inspection beyond what he can see?
Biggest problem I have seen in some of the sprinkler companies I've been
involved with is that most of your inspectors are ex-fitters who got
promoted. They have no real design or engineering background so they
couldn't tell an owner if something was improperly designed or
installed. Now this isn't true in 100% of the cases but in most.
If the job is improperly managed by the sprinkler contractor, the design
and installation deficiencies are usually brought to light during fire
marshal or underwriter inspections, sometimes.
You wouldn't believe how many industrial plants I've walked through and
just cringed at the installations. Code compliant, pfffft, yeah right
maybe the DaVinci Code or Cap'n Crunches Secret Code, but definitely not
NFPA or building codes. But the owner isn't an expert so he wouldn't
know that someone took liberties and he did select the lowest bidder you
now.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, January 11, 2007 11:47 AM
To: [email protected]
Subject: RE: Testing
Rod,
With all due respect, Section 1.1 (Scope) of NFPA-25 reads "This
standard applies to fire protection systems that have been properly
installed in accordance with generally accepted practices". That's
rather ambiguous but lets just assume that NFPA-25 is speaking of
standards such as NFPA 13 & 13R. (PS lets hope so because FM Globals
requirements could also be interpreted as "generally accepted
practices")
With that said is it not true that a determination by the maintenance
contractor is needed to assure that the system(s) being maintained "have
been properly installed" in order for NFPA-25 to apply ?.
The scoping statement is very clear, systems that have not been properly
installed are outside the scope of NFPA-25 so in effect an NFPA-25
inspection of an improperly installed system is null and void.
My point in this discussion is that the ultimate fire protection goal is
to assure the health, welfare and safety of building occupants and
property protection where applicable. When a building owner or an AHJ
receives a certificate of inspection from a contractor they assume the
system will control a fire as designed by the applicable standard not
that an unprotected area or deficiency was ignored simply because of the
fine print of the maintenance standard. If that's the case an annual
inspection by a qualified fire protection engineer is in order.
Sincerely in the interest of Fire Safety,
John Drucker
Fire Protection Subcode Official (AHJ)
Borough of Red Bank, NJ
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of rod
Sent: Thursday, January 11, 2007 11:00 AM
To: [email protected]
Subject: RE: Testing
John,
I agree with you that there are some real problems with the inspections,
inspectors and enforcers. I do not believe however that we can get into
a situation where even NICET trained certified inspectors are getting
into "protection deficiencies". This is a slippery slope and creates a
liability for the contractor that NFPA 25 quite frankly puts on the
owner. To transfer that liability to the contractor for $200 is not
equitable. The only people with a "false" sense of security are those
that do not read the NFPA 25.
Rod DiBona
Rapid Fire
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Wednesday, January 10, 2007 4:34 PM
To: [email protected]
Subject: RE: Testing
New Jersey has extensive certification & licensing regulations for fire
protection contractors. However coordination rarely occurs and flow and
tamper switches are still be "tested" by alarm technicians moving
actuator arms. I recently attained a flow switch improperly installed in
a copper tee to the extend the vane wasn't even in the water stream yet
the "fire alarm inspection report" noted this device as functional even
so far as listing the time delay.
Whats need in this situation is a requirement where only alarm companies
and or sprinkler companies be permitted to perform inspection in testing
in suppressed/alarmed buildings that posess certification in BOTH
disciplines.
The reality is that even with NFPA-13, 72 and 25 gross errors and
omissions are occuring during periodic inspections and tests.
Inspectors should know how to identify protection deficiencies not just
installation and maintenance deficiencies. NFPA-25 certifications give a
false sense of security.
John Drucker
Fire Protection Subcode Official
New Jersey
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Wednesday, January 10, 2007 4:20 PM
To: [email protected]
Subject: RE: Testing
Tennessee where I work requires licensing.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Brown
Sent: Wednesday, January 10, 2007 3:52 PM
To: [email protected]
Subject: RE: Testing
But when you look at the number of states that have a license
requirement they are few. There are many of the larger cities have
requirements but not as a state. Look at Oklahoma, They have one of the
best licensing requirements I am aware of and they enforce it well for
both the fire alarm and fire sprinkler industries. I think every state
should be looking at what the State of Oklahoma is requiring. Look at
the web site for Oklahoma Department of Health of the requirements if
interested. They are doing the right thing! Every one associated with
fire protection has to be licensed.
Thank you,
Chris Brown
Fire Protection Designer, Poole Fire Protection
Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600 Fax:
913.829.8690
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, January 10, 2007 2:37 PM
To: [email protected]
Subject: Re: Testing
there is a fine point you are missing. The OWNER of a PRIVATE facility
is typically allowed to do as much of their own work as they want to.
It's when you hire out to do work for someone else that licensing enters
the equation.
Roland
On Jan 10, 2007, at 12:29 PM, <[EMAIL PROTECTED]> wrote:
Chris, Kansas isn't alone on that. I have a project in a nearby
state.
The owner wanted to do the installation himself. He has mechanics
that know how to use a pipe wrench. (this guy wanted a detail on his
drawings of how to install an upright head, yes we are in
trouble.......)
Anyway, when I called the state board of licensure and asked the lady
if you had to be specifically licensed to install sprinkler systems
her words were, "that's a good question, I don't know", so she passed
me off to her department manager, who obviously read from the same
script
because he said the same thing. Seems in their state and local
municipality don't require permits or system inspections and so anyone
can install it.
There is no consistency in the laws concerning licensing.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax -
864.599.8439 [EMAIL PROTECTED] http://www.lg.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Brown
Sent: Wednesday, January 10, 2007 3:17 PM
To: [email protected]
Subject: RE: Testing
In the state of Kansas all you need is transportation to the site it
even could be by mass transit and you can work on any type of fire
protection system. Wichita has some requirements and Kansas City
Missouri has a sprinkler contractors license requirement but other
than that any one can work on any fire protection system. We have
plumbers installing sprinkler systems and electricians installing fire
alarm system. They don't even know what NFPA is.
Thank you,
Chris Brown
Fire Protection Designer, Poole Fire Protection
Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600
Fax:
913.829.8690
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg
Fontes
Sent: Wednesday, January 10, 2007 1:56 PM
To: [email protected]
Subject: Testing
Does a C-10 and/or electrical/alarm contractors license allow them to
contract the testing of water base fire protection systems? (I.E.
opening inspectors test valves, operating control valves, testing of
Pre-action/Deluge/Dry systems, generally can they operate any
component of a fire sprinkler system that has an alarm affiliated with
it?)
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum