Thom,
We all know that George doesn't sleep at night.  Coffee and cigarettes
man!
Nothing gets by that guy :-)

Terri Simmons Leyton
PROTECTION DESIGN & CONSULTING
voice:  858.751.2930
fax:  858.751.2933
cell:  619.871.8450

-----Original Message-----
From: Thom McMahon [mailto:[EMAIL PROTECTED] 
Sent: Thursday, January 11, 2007 2:10 PM
To: [email protected]
Subject: Re: Testing

George! You sleep at night? I took a nap in 1973, and still worry I
missed 
something that will bite me in the ass.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "George Church" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, January 11, 2007 10:48 AM
Subject: RE: Testing


> Hmmm. More to the point brought up that inspections of improperly 
> installed
> (or designed) systems are now null and void.
>
> Well, I don't know your confidence level, but from what I've seen, we
are
> NOT a perfect industry. Day in and day out, gray areas and fitter 
> mistakes,
> design mistakes, fab errors, wrong heads show up and get installed,
duct
> changes, architectural changes- all these combine so I can about
guarantee
> you that virtually NO systems installed are "perfect". I don't expect
any
> argument from anyone on this. Therefore, the systems we install are
not
> compliant with NFPA #13- if you were to take a fine-tooth comb and go
thru
> EVERYTHING. I'm not saying, and out industry's amazingly great track 
> record
> doesn't argue, that the systems aren't good, aren't workable, and
aren't
> REASONABLY compliant.
>
> BUT
> Any of us who have been involved in lawsuits will agree that all
common
> sense and what is "generally accepted" can quickly go out the window
in a
> court of law and the most inane arguments can win. I had a
competitor's
> lawyer argue
> a) that I wasn't competent to testify on the subject of inspections
and
> whether a system was compliant  and
> b) that NFPA #13 was NOT part of the city's fire code.
> Understand the system we're talking about was installed to protect a 
> grocery
> store, was designed to light hazard occupancy (by a Level IV) using
the
> largest room rule (ignoring the sales floor since the largest room was
> "remote"- and wasn't even a room, it was a ceiling elevation change.
The
> system demand was 66 GPM plus 100 GPM hose allowance, the "backflow"
was a
> pair of plumber's brass swing cheks (2") between 1/4 turn ball valves,

> with
> a 1.5" residential FDC. Did I mention the combo ITC/main drain was a
3/4"
> boiler drain stuck in a FIT tee above the "BFP" ?  My dog is competent
to
> tell you this system is non-compliant. And this was a different one
than 
> the
> CPVC system installed by same guy, guess he's just not very good at
> mercantile. Ironically, he complains how others violate the code!
>
> So when we go inspect a system, or deeper, perform a full gamut of ITM

> (and
> there's an interesting dilemma- quote ITM when your competitor quotes
I 
> and
> you will be high bidder) - and since it's noncompliant, I'm outside
NFPA 
> #25
> when the place burns down.
>
> AARRRGHHHHHHHHHHHH how do we owners sleep at night?
>
> George Church
> Rowe Sprinkler
>
>
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
> [EMAIL PROTECTED]
> Sent: Thursday, January 11, 2007 12:14 PM
> To: [email protected]
> Subject: RE: Testing
>
> John, I believe what you said has merit to a point.  I believe that
> every inspection should entail more than just ringing the bell.
> Unfortunately that's all a lot of owners want to pay for and that what
a
> lot of inspectors do.  It's a fast easy way to make a buck.
>
> The inspection should point out any obvious visible deficiencies but
to
> what degree would or could and engineer perform any kind of absolutely
> certifiable inspection beyond what he can see?
>
> Biggest problem I have seen in some of the sprinkler companies I've
been
> involved with is that most of your inspectors are ex-fitters who got
> promoted.  They have no real design or engineering background so they
> couldn't tell an owner if something was improperly designed or
> installed.  Now this isn't true in 100% of the cases but in most.
>
> If the job is improperly managed by the sprinkler contractor, the
design
> and installation deficiencies are usually brought to light during fire
> marshal or underwriter inspections, sometimes.
>
> You wouldn't believe how many industrial plants I've walked through
and
> just cringed at the installations.  Code compliant, pfffft, yeah right
> maybe the DaVinci Code or Cap'n Crunches Secret Code, but definitely
not
> NFPA or building codes.  But the owner isn't an expert so he wouldn't
> know that someone took liberties and he did select the lowest bidder
you
> now.
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.lg.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of John
> Drucker
> Sent: Thursday, January 11, 2007 11:47 AM
> To: [email protected]
> Subject: RE: Testing
>
> Rod,
>
>
> With all due respect, Section 1.1 (Scope) of NFPA-25 reads "This
> standard applies to fire protection systems that have been properly
> installed in accordance with generally accepted practices".  That's
> rather ambiguous but lets just assume that NFPA-25 is speaking of
> standards such as NFPA 13 & 13R.  (PS lets hope so because FM Globals
> requirements could also be interpreted as "generally accepted
> practices")
>
> With that said is it not true that a determination by the maintenance
> contractor is needed to assure that the system(s) being maintained
"have
> been properly installed" in order for NFPA-25 to apply ?.
>
> The scoping statement is very clear, systems that have not been
properly
> installed are outside the scope of NFPA-25 so in effect an NFPA-25
> inspection of an improperly installed system is null and void.
>
> My point in this discussion is that the ultimate fire protection goal
is
> to assure the health, welfare and safety of building occupants and
> property protection where applicable.  When a building owner or an AHJ
> receives a certificate of inspection from a contractor they assume the
> system will control a fire as designed by the applicable standard not
> that an unprotected area or deficiency was ignored simply because of
the
> fine print of the maintenance standard.  If that's the case an annual
> inspection by a qualified fire protection engineer is in order.
>
> Sincerely in the interest of Fire Safety,
>
> John Drucker
> Fire Protection Subcode Official (AHJ)
> Borough of Red Bank, NJ
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of rod
> Sent: Thursday, January 11, 2007 11:00 AM
> To: [email protected]
> Subject: RE: Testing
>
> John,
>
> I agree with you that there are some real problems with the
inspections,
> inspectors and enforcers. I do not believe however that we can get
into
> a situation where even NICET trained certified inspectors are getting
> into "protection deficiencies". This is a slippery slope and creates a
> liability for the contractor that NFPA 25 quite frankly puts on the
> owner. To transfer that liability to the contractor for $200 is not
> equitable. The only people with a "false" sense of security are those
> that do not read the NFPA 25.
>
> Rod DiBona
> Rapid Fire
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of John
> Drucker
> Sent: Wednesday, January 10, 2007 4:34 PM
> To: [email protected]
> Subject: RE: Testing
>
> New Jersey has extensive certification & licensing regulations for
fire
> protection contractors. However coordination rarely occurs and flow
and
> tamper switches are still be "tested" by alarm technicians moving
> actuator arms. I recently attained a flow switch improperly installed
in
> a copper tee to the extend the vane wasn't even in the water stream
yet
> the "fire alarm inspection report" noted this device as functional
even
> so far as listing the time delay.
>
> Whats need in this situation is a requirement where only alarm
companies
> and or sprinkler companies be permitted to perform inspection in
testing
> in suppressed/alarmed buildings that posess certification in BOTH
> disciplines.
>
> The reality is that even with NFPA-13, 72 and 25 gross errors and
> omissions are occuring during periodic inspections and tests.
> Inspectors should know how to identify protection deficiencies not
just
> installation and maintenance deficiencies. NFPA-25 certifications give
a
> false sense of security.
>
> John Drucker
> Fire Protection Subcode Official
> New Jersey
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Bill
> Minkel
> Sent: Wednesday, January 10, 2007 4:20 PM
> To: [email protected]
> Subject: RE: Testing
>
> Tennessee where I work requires licensing.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Chris
> Brown
> Sent: Wednesday, January 10, 2007 3:52 PM
> To: [email protected]
> Subject: RE: Testing
>
> But when you look at the number of states that have a license
> requirement they are few. There are many of the larger cities have
> requirements but not as a state. Look at Oklahoma, They have one of
the
> best licensing requirements I am aware of and they enforce it well for
> both the fire alarm and fire sprinkler industries. I think every state
> should be looking at what the State of Oklahoma is requiring. Look at
> the web site for Oklahoma Department of Health of the requirements if
> interested. They are doing the right thing! Every one associated with
> fire protection has to be licensed.
>
>
> Thank you,
>
> Chris Brown
> Fire Protection Designer, Poole Fire Protection
> Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600
Fax:
> 913.829.8690
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Roland
> Huggins
> Sent: Wednesday, January 10, 2007 2:37 PM
> To: [email protected]
> Subject: Re: Testing
>
> there is a fine point you are missing.  The OWNER of a PRIVATE
facility
> is typically allowed to do as much of their own work  as they want to.
> It's when you hire out to do work for someone else that licensing
enters
> the equation.
>
> Roland
>
> On Jan 10, 2007, at 12:29 PM, <[EMAIL PROTECTED]> wrote:
>
>> Chris, Kansas isn't alone on that.  I have a project in a nearby
>> state.
>> The owner wanted to do the installation himself.  He has mechanics
>> that know how to use a pipe wrench.  (this guy wanted a detail on his
>> drawings of how to install an upright head, yes we are in
>> trouble.......)
>>
>> Anyway, when I called the state board of licensure and asked the lady
>> if you had to be specifically licensed to install sprinkler systems
>> her words were, "that's a good question, I don't know",  so she
passed
>
>> me off to her department manager, who obviously read from the same
>> script
>> because he said the same thing.   Seems in their state and local
>> municipality don't require permits or system inspections and so
anyone
>
>> can install it.
>>
>> There is no consistency in the laws concerning licensing.
>>
>> Craig L. Prahl, CET
>> Fire Protection Group
>> Mechanical Department
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
>> 864.599.8439 [EMAIL PROTECTED] http://www.lg.com
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Chris
>> Brown
>> Sent: Wednesday, January 10, 2007 3:17 PM
>> To: [email protected]
>> Subject: RE: Testing
>>
>> In the state of Kansas all you need is transportation to the site it
>> even could be by mass transit and you can work on any type of fire
>> protection system. Wichita has some requirements and Kansas City
>> Missouri has a sprinkler contractors license requirement but other
>> than that any one can work on any fire protection system. We have
>> plumbers installing sprinkler systems and electricians installing
fire
>
>> alarm system. They don't even know what NFPA is.
>>
>>
>> Thank you,
>>
>> Chris Brown
>> Fire Protection Designer, Poole Fire Protection
>> Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600
>> Fax:
>> 913.829.8690
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Gregg
>> Fontes
>> Sent: Wednesday, January 10, 2007 1:56 PM
>> To: [email protected]
>> Subject: Testing
>>
>> Does a C-10 and/or electrical/alarm contractors license allow them to
>> contract the testing of water base fire protection systems?  (I.E.
>> opening inspectors test valves, operating control valves, testing of
>> Pre-action/Deluge/Dry systems, generally can they operate any
>> component of a fire sprinkler system that has an alarm affiliated
with
>
>> it?)
>>
>> Gregg Fontes
>> Cen-Cal Fire Systems, Inc.
>> 209-334-9119
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to