Thanks for update on changes to the 13-2007 and the clarification of issues 
with respect to terminology.

--
David de Vries, P.E., CSP 
Firetech Engineering Incorporated 
[EMAIL PROTECTED]

-------------- Original message -------------- 
From: Roland Huggins <[EMAIL PROTECTED]> 

> You are crossing the wires on flame spread and limited combustible. 
> IT is amusing that NFPA 13 has an interesting and illogical 
> application of the terms in the 02 edition. For a concealed 
> COMBUSTIBLE space, rigid material with a Class A flames spread OR 
> lumber that has been treated with a fire retardant (which typically 
> creates a Class A flame spread does it not?) allows omission of 
> sprinklers. Limited combustible enters the discussion when we start 
> talking about exterior roofs and canopies. Keep in mind that exterior 
> canopies is just addressing protection BENEATH them. This is where 
> you encounter the requirement for limited combustible construction in 
> order to omit protection from BENEATH the canopy. 
> 
> The 07 edition has finally acknowledges separation and protection of 
> the concealed spaces makes a difference. It also as incorporated the 
> allowance for fire retardant treated lumber to omit protection so the 
> oddity in how the two characteristics are treated in prior editions 
> has been addressed. 
> 
> Roland 
> 
> 
> 
> On Jan 12, 2007, at 7:47 AM, David de Vries/Firetech wrote: 
> 
> > Todd: 
> > 
> > That appears to be UL, not ULC. 
> > 
> > Whether this product, or any other product listed in that category 
> > would turn a ceiling or concealed space that is otherwise 
> > combustible into a non-combustible or limited combustible ceiling 
> > or space is problematic. The test applied by UL is the one for 
> > Surface Burning Characteristics, UL 723. It does not necessarily 
> > correlate to the flammability of the material. For example, gypsum 
> > board with typical paper face might have a flame spread index of 10 
> > or 15, just like a wood product treated with one of these fire 
> > retardants. The difference is that the core material of the gyp 
> > board is non-combustible, whereas the wood product is combustible. 
> > Once the surface protection is gone, you're back to a combustible 
> > concealed space, or combustible ceiling. 
> > 
> > -- 
> > David de Vries, P.E., CSP 
> > Firetech Engineering Incorporated 
> > [EMAIL PROTECTED] 
> > 
> > -------------- Original message -------------- 
> > From: Todd Williams - work 
> > 
> >> Bill, 
> >> 
> >> Is this UL or UL Canada listed? 
> >> 
> >> At 09:23 AM 1/12/2007, you wrote: 
> >>> This product has a UL listing. I'm not endorsing one way or the 
> >>> other but I 
> >>> think the intent of NFPA 13 would be to accept products like this 
> >>> when 
> >>> applied properly as Roland indicates. 
> >>> 
> >>> http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/ 
> >>> showpage.html?name 
> >>> =BMQX.R19565&ccnshorttitle=Coatings,+Fire 
> >>> +Retardant&objid=1078153113&cfgid=1 
> >>> 073741824&version=versionless&parent_id=1073984654&sequence=1 
> >>> 
> >>> Bill Brooks 
> >>> Pittsburgh, PA 
> >>> 
> >>> -----Original Message----- 
> >>> From: [EMAIL PROTECTED] 
> >>> [mailto:[EMAIL PROTECTED] Behalf Of Roland 
> >>> Huggins 
> >>> Sent: Thursday, January 11, 2007 1:13 PM 
> >>> To: [email protected] 
> >>> Subject: Re: Wood Coating 
> >>> 
> >>> 
> >>> AS we all know, 13 allows fire retardant wood to be used as defined 
> >>> by NFPA 703. The last time I looked (was nit recently but a year or 
> >>> 3), NFPA 703 addresses both pressure treated wood (as required by 
> >>> the 
> >>> building code to qualify as treated) AND surface applied (ie field 
> >>> painted). 
> >>> 
> >>> IMHO, bad approach. 
> >>> 
> >>> Roland 
> >>> 
> >>> On Jan 10, 2007, at 2:09 PM, Todd Williams - work wrote: 
> >>> 
> >>>> I had a architect ask me about using this in a combustible church 
> >>>> attic. I was skeptical and did a little investigating. The tests 
> >>>> that produced the results had a minimum film thickness in order to 
> >>>> work properly. How do you verify the minimum thickness in a field 
> >>>> application? My guess is that the tests shown (by UL Canada only) 
> >>>> were not done on assembled structures, but on individual pieces of 
> >>>> material that were coated under near ideal conditions. What would 
> >>>> happen in a structure coated after assembly? Why is there no UL - 
> >>>> United States or FM tests? Too many questions for me; I'd walk 
> >>>> away. (So did the architect referenced above) 
> >>>> 
> >>>> Todd 
> >>>> 
> >>>> At 04:15 PM 1/10/2007, you wrote: 
> >>>>> Has anyone seen this product? 
> >>>>> It touts that it replaces sprinklers in combustible concealed 
> >>>>> spaces, 
> >>>>> under NFPA-13. 
> >>>>> If you have seen it, pros and cons? 
> >>>>> 
> >>>>> http://www.eaglecoatings.net/content/safecoatlatex.htm 
> >>>>> 
> >>>>> 
> >>>>> Wayne Automatic Fire Sprinklers, Inc. 
> >>>>> 2006 Inductee into "The Players Hall of Fame" 
> >>>>> at The Great Games of Business 
> >>>>> Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work" 
> >>>>> Rated #1 in 2006 
> >>>>> Large Business Category 
> >>>>> by Orlando Business Journal 
> >>>>> _______________________________________________ 
> >>>>> Sprinklerforum mailing list 
> >>>>> [email protected] 
> >>>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> >>>> 
> >>>> Todd G. Williams, PE 
> >>>> Fire Protection Design/Consulting 
> >>>> Stonington, Connecticut 
> >>>> 860-535-2080 
> >>>> www.fpdc.com 
> >>>> _______________________________________________ 
> >>>> Sprinklerforum mailing list 
> >>>> [email protected] 
> >>>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> >>>> 
> >>> 
> >>> _______________________________________________ 
> >>> Sprinklerforum mailing list 
> >>> [email protected] 
> >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> >>> _______________________________________________ 
> >>> Sprinklerforum mailing list 
> >>> [email protected] 
> >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> >> 
> >> Todd G. Williams, PE 
> >> Fire Protection Design/Consulting 
> >> Stonington, Connecticut 
> >> 860-535-2080 
> >> www.fpdc.com 
> >> 
> >> _______________________________________________ 
> >> Sprinklerforum mailing list 
> >> [email protected] 
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > _______________________________________________ 
> > Sprinklerforum mailing list 
> > [email protected] 
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
> > 
> 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to