It's not that we don't care what our competition is doing, We already know, like you, that they don't follow every rule and letter of the code, and have decided not to take that road.(We always endeavor to make a sincere effort to do what's required, or what's Right.)(Are we always able to fulfill that goal? No but we try, and are more successful than those that follow others they know or believe to be less mindful.) Does it cost us money and job's? You bet ya! But it also provides us opportunities to teach both the GC's and AHJ's what to look for, and how it should be done. I know that all sounds good, on a gut level, but the truth is it bugs the [EMAIL PROTECTED] out of me when we lose work to someone that doesn't do it right! Guess I'll just keep rolling that stone up the hill, cause the alternative is to let it crush us.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Greg McGahan" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, January 15, 2007 11:06 AM
Subject: RE: hydraulic elevators


One LAST comment on this thread...

My intent was to find out what the rest of the country was doing. I think I
did that.

Thanks. However, if AHJ's are confused - and they are - then clarification
should be made by NFPA. If the intent is to require the sprinklers because
of collected debris and hydraulic fluid combined the they should simply say
so and help the AHJ's understand and therefore help the
contractors/engineers and ensure that the INTENT of the code is met rather
than just blindly doing sometimes expensive, awkward, difficult things
without understanding why.

And to hear some of you guys talk, it sounds like you could care less about
what your competition is doing when you bid and/or design projects. I
believe it is good business - and yes, I am counting dollars - to make sure
that we are doing things correctly while we are making money and making
money as we do things correctly. It will not benefit me, my partners,
employees or I dare say this industry to lose money and close down because
we are unarmed to answer questions like this intelligently when they come up and we simply do everything right while our weak minded competitors stay in
business doing things wrong.

Is there not a benefit in knowing which battles are worth fighting hard for
and which ones may have less of an impact on a system if the AHJ is not
requiring it?

We have been and will continue to protect elevator shafts. Thanks for the
input.

Greg
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Thursday, January 11, 2007 4:41 PM
To: [email protected]
Subject: Re: hydraulic elevators

I just get the feeling this discussion to eliminate the bottom of shaft
heads, is just another step backwards, if we actually start to eliminate
sprinkler heads, based upon weather or not we've had x number of
activations, or "no fire deaths in un-sprinklerd spaces"

If we start to delete sprinklers from areas, lets do so because A) it can't
burn. B) there is no ignition source. and C) there is no fuel.

I mean it really guy's when is the last time you heard of someone who Died
in a janitors closet? Yet we protect them, and well we should since fires
start there, and can spread to the rest of the building. When in doubt put
in the sprinkler head.

As a contractor, I'd rather put in a few extra heads on every job that
weren't "Required" (Gray area) rather than miss even one that was. It's that

One which can turn the court room into a "Life changing experience"

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "David de Vries/Firetech" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, January 10, 2007 10:14 PM
Subject: RE: hydraulic elevators


Agreed.  For the sprinkler to activate, the ceiling needs to be there for
both fuel sources:  debris or hydraulic fluid.

John, now as to your contention that most times the car rests at the
terminal floor, I guess your luck with elevators is better than mine.
Seems whenever I go into to a multi-story building, the elevators are all
near the top of the building!!

I would still love to hear from contractors as to how many of those
sidewalls they have changed due to a fire in the pit. And, George, I know

about that form in the back of the book, so if I get the data I will
submit the proposal to 13.

--
David de Vries, P.E., CSP
Firetech Engineering Incorporated
[EMAIL PROTECTED]

-------------- Original message -------------- From: "John Drucker" <[EMAIL PROTECTED]>

David,

The same "no ceiling" situation would hold true for fires involving
combustible hydraulic fluids. But consider that most times an elevator
car
"rests" at the terminal floor at or a floor above the pit creating the
requisite thermal barrier.

John Drucker
Fire Protection Subcode Official
New Jersey



-----Original Message----- From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David de
Vries/Firetech
Sent: Wednesday, January 10, 2007 3:06 PM
To: [email protected]
Subject: RE: hydraulic elevators

Bill:

You raise a good point -- what is the fire loss experience in elevator
shafts?

Do we have a history of such fires? (Probably do, with debris then
cigarets
dropped down the gap between the cab and the floor.)
How often does a sidewall sprinkler activate when there is such a fire?
Was the elevator cab at its lowest position such that heat from the fire
could activate the sprinkler? (If we have no "ceiling" to direct the heat
to the sprinkler, unless the fire is directly below the sprinkler, it
will
probably not activate.)

If no contractor on this forum has ever been called out to restore a
system
(change out the one sidewall sprinkler) after a fire in the pit of an
elevator, hydraulic or traction, then the 13 committee needs to know.
Maybe
we can do without one there.

--
David de Vries, P.E., CSP
Firetech Engineering Incorporated
[EMAIL PROTECTED]

-------------- Original message -------------- From: "Brooks, Bill"

> Nothing the committee does is contradictory (by definition)! It only
> appears contradictory until there is an explanation that makes the
apparent
> contradiction plausible.
>
> So...
>
> It appears the committee is saying:
>
> 1. Debris - combustible fluid = no hazard
> 2. Debris + combustible fluid = hazard
>
> By itself, any quantity of accumulated debris is not a hazard. > Wouldn't
> this be borne out by past experience? Does this remove the
> contradiction?
>
> Bill Brooks
> Pittsburgh, PA
>
> -----Original Message----- > From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] Behalf Of John
> Drucker
> Sent: Monday, January 08, 2007 1:42 PM
> To: [email protected]
> Subject: RE: hydraulic elevators
>
>
> The NFPA-13 hoistway pit suppression requirement is contradictory. The
> explanatory material states; " The sprinklers in the pit are intended
> to
> protect against fires caused by debris, which can accumulate over
> time."
> The exception permits the omission of sprinklers in hoistway pits that
> are enclosed, of non combustible construction and that do not contain
> combustible hydraulic fluids. So what happened to the debris ?. The
> removal of combustible hydraulic fluids does not alleviate the debris
> issue. A hazard still exists.
>
> Additionally the non combustible fluid issue is not addressing
> hydraulic
> elevators but rather traction elevators that don't utilize hydraulics
> as
> their means of locomotion.
>
> John Drucker
> Fire Protection Subcode Official
> New Jersey
>
>
> -----Original Message----- > From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Roland
> Huggins
> Sent: Monday, January 08, 2007 1:17 PM
> To: [email protected]
> Subject: Re: hydraulic elevators
>
> the problem with hydraulic oil is not how well it burns in standard
> liquid form (ie flash point). It's when a small leak occurs under
> pressure and you get atomized oil spraying out. As a comparison,
> grain dust laying on the ground is not that big a deal but when
> floating in the air, can go boom.
>
> Roland
>
> On Jan 8, 2007, at 9:57 AM, Loren Johnson wrote:
>
> > In my dealings with FM Global, their Approval Guide
> > does list manufacturers who have a less hazardous type
> > of hydraulic fluid, which has a higher flash point
> > than normal hydraulic fluids. FM indicates that these
> > too will burn under certain conditions, but the fire
> > risk has been reduced to an acceptable degree.
> >
> > Loren Johnson - CFPS, CET
> > Fire Protection Systems Consultant
> > The Hitchcock Company
> > Peoria, IL
> > --- [EMAIL PROTECTED] wrote:
> >
> >> I had been told by one elevator inspector that there
> >> was an FM approved
> >> hydraulic media that was non-combustible and if that
> >> was being used the
> >> sprinkler in the pit could be deleted.
> >>
> >> On the other hand in another jurisdiction I was told
> >> that regardless of
> >> the hydraulic media used that we were to provide a
> >> sprinkler in the pit
> >> due to the possible accumulation of miscellaneous
> >> debris which could
> >> catch fire.
> >>
> >>
> >> Isn't it wonderful to be in an industry where
> >> everything is so black and
> >> white? ;)
> >>
> >>
> >>
> >> Craig L. Prahl, CET
> >> Fire Protection Group
> >> Mechanical Department
> >> CH2MHILL
> >> Lockwood Greene
> >> 1500 International Drive
> >> PO Box 491, Spartanburg, SC 29304-0491
> >> Direct - 864.599.4102
> >> Fax - 864.599.8439
> >> [EMAIL PROTECTED]
> >> http://www.lg.com
> >>
> >>
> >> -----Original Message----- > >> From: [EMAIL PROTECTED]
> >> [mailto:[EMAIL PROTECTED] On
> >> Behalf Of George
> >> Church
> >> Sent: Monday, January 08, 2007 10:41 AM
> >> To: [email protected]
> >> Subject: RE: hydraulic elevators
> >>
> >> Perhaps everyone else in the area installs to #13R ?
> >> Perhaps a call to the local AHJ(s) would clear up
> >> whether you're the
> >> only one doing it correctly, in which case maybe
> >> your competitors will
> >> be a little dismayed to find themselves going back
> >> and retrofitting
> >> their bottoms. The call to the AHJ(s) could be
> >> two-fold: ask them if
> >> they believe it should be required; and ask WHY it
> >> is not- you may find
> >> in the near future you're no longer alone in the
> >> shaft.
> >>
> >> George Church
> >> Rowe Sprinkler
> >>
> >> -----Original Message----- > >> From: [EMAIL PROTECTED]
> >> [mailto:[EMAIL PROTECTED] On
> >> Behalf Of David de
> >> Vries/Firetech
> >> Sent: Monday, January 08, 2007 10:30 AM
> >> To: [email protected]
> >> Subject: Re: hydraulic elevators
> >>
> >> Pat on the back to the only contractor in the area
> >> complying with this
> >> provision of 13.
> >>
> >> -- > >> David de Vries, P.E., CSP
> >> [EMAIL PROTECTED]
> >>
> >> -------------- Original message -------------- > >> From: "Greg McGahan"
> >>
> >>>
> >>> We are receiving mixed reviews from AHJ's
> >> regarding this issue: Are
> >>> sprinklers required in the bottom of hydraulic
> >> elevator shafts?
> >>>
> >>> I know what the code says but we have never been
> >> able to document that
> >>
> >>> ANY
> >>
> >>> hydraulic elev fluid is non-combustible by
> >> definition. I was informed
> >>> this
> >>
> >>> morning that we are the only contractor in the
> >> area putting sprinklers
> >>
> >>> in the bottom of these shafts.
> >>>
> >>> Thanks,
> >>> Greg McGahan
> >>>
> >>>
> >>>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >
> >
> > __________________________________________________
> > Do You Yahoo!?
> > Tired of spam? Yahoo! Mail has the best spam protection around
> > http://mail.yahoo.com
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to