NO. As the tank empties or reduces to zero this head disappears. Assume the
tank is nearly empty. That is the static head. If the tank is on a hill the
elevation from base of the tank will provide you some static head.
Art
ATCO FIRE/Tiroly & Associates

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Leif Glans
Sent: Monday, January 15, 2007 12:26 PM
To: [email protected]
Subject: Positive static head for tanks

Hi!

If one uses Centrifugal Pump according to NFPA 20, one should not use it if
static suction lift is required (6.1.2, A 6.1.2)

According to NFPA 22 4.1.3 for suctions tanks, the net capacity shall be the
number of cubic meters (U.S. gallons) between the inlet of the overflow and
the inlet of the vortex plate 

Is all of this volume considered positive head according to NFPA?



Best regards/ Leif Glans

www.lg-sprinklerkonsulten.com

LG Sprinklerkonsulten
PG Vejdes vag 15
351 96 Vaxjo

Sweden

Phone: +46 470-74 50 25
Fax: +46 470-74 50 26
Cell: +46 734-28 13 10