Gentlemen and /or Ladies:

The restriction on velocities was introduced by FM back when grids first
came into use.  Automatic and Grinnell in years past always used a
maximum velocity of 32 fps that came from some old studies of water
mains.  When grids first started, contractors, and I was one,
immediately started pushing the envelope with 1" grids all over the
place.  FM decided that to use the 20 fps requirement on grids.  Later
they modified the requirement to apply to the branch line but not the
riser nipples.  There has never been a requirement for a maximum
velocity in NFPA 13 to my knowledge.  The hydraulic formulas and the C
factors have a safety factors built in.  Of more importance in a lot of
cases is the reliability the water supply and the accuracy of the water
test used in the calculations.  Water tests and water supplies are often
the least researched part of the design.  In many parts of the country
the AHJ's impose a limit by insisting on a cushion of some kind.  It
parts of Florida the AHJ's do not allow more than 50 psi static pressure
to be used in the calculations period regardless of the water test
results.  It seems to me that you may be gagging on a nat and swallowing
an elephant.  If you are concerned specify a cushion be allowed and do
not calculate the demand to the maximum available water supply.  Specify
a particular psi cushion.

If you want a system to last forever just specify Schedule 40 pipe and
do not allow thin wall pipe but the cost of the system will go up and
the owner may not be happy that he has to pay more.

Michael L. Brown

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Monday, January 15, 2007 2:26 PM
To: [email protected]
Subject: RE: max velocity

Given the long life and "who knows what may happen" alterations, you're
using velocity as a built-in hedge against -well-who knows? But
consistently
applied, you'll end up mtg the criteria important to the owner- trying
to
make a system that's as idiot-proof as possible.  Do you also limit
spacing?
If walls are going to be added, it makes it handier for those who don't
have
pilot hole clamps and snaplets to add heads if there's an outlet with
5'.

It is a pain to go in and change wet systems to C=100, and an
alternative
method would be to simply specify a larger cushion, either in % or 20
PSI.
Perhaps tailor it to the building and what characteristics the servicing
water purveyor has, whether it's a mature area, or growing wildly so
expectations would be that it'll be degrading quickly. But with a 50
year
life- that's hard. As my friend Steve pointed out, did anyone think
bottled
water would be a zillion dollar a year industry several years ago? Heck,
that's almost as long as Thom's been in sprkrs!


glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Monday, January 15, 2007 1:55 PM
To: [email protected]
Subject: RE: max velocity


Folks,
Here is some more food for thought.  I provide the sprinkler
specification
for all of my federal projects.  I use 20 fps velocity as a limit and a
maximum C of 100 to insure that I have a system that has a chance to
last
for the life of the building (approximately 50+ years).  Our buildings
are
always being changed with the sprinkler system being drained and
modified
many many times by all sorts of contractors, from the best to the worst.
Once the building is constructed and occupied, the local GSA service
center
does all of the work in the building, usually with the lowest bidder.

Therefore, we need some sort of hedge against all of this.  Once the
building is built, it is out of my control.  I see no problem specifying
these limits as long as everyone is bidding the same job.

Any suggestions?

Thank You

Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to