Thom,

I just got off the phone wirth an AHJ moments before I read your
comment doing exactly what you are suggesting. In my case it was a
three story building (the lowest half below grade) connected to a two
story building by a breezeway on a slope with ground level for the two
story being at the same level as the roof of three story. Since they
were connected and on the same property (essentially the samr
building) he started out considering this a five story building with a
more complex standpipe system than usually encountered. After a chat
about fire department access, hydrant location, and tactics the
standpipe completely disappeared. ALWAYS, as you say, discuss your
plan with the end user.

On 1/30/07, Thom McMahon <[EMAIL PROTECTED]> wrote:
As Steve has always reminded me, the "End User" or customer for a Standpipe
is the Fire Department. This is one of the few times when the AHJ is also
the user. ALWAYS! Ask them what they want, and why. It could be very
educational, and save a lot of headache and lost revenue.
We had a project today with Split Level access to the stairwell. Went to the
AHJ discussed our concerns on standpipe location, Mid vs. Floor landings and
which were both, as well as roof access. Guess what? They spotted the
standpipe locations on our drawing and we're off to other money making
projects. We 'll put them where they asked, and move on. (It makes life so
simple when you can just give the AHJ some voice, and give them what they
want up front.)

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Steve Leyton" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, January 30, 2007 2:02 PM
Subject: RE: NFPA #14 and pressures


>I think that the sections I referenced are quite clear:
>
> "For Class III systems installed without hose, the water supply
> requirements shall be as specified for Class I systems."
>
> That would be ALL of the water supply design criteria, including both
> maximum and minimum pressures.
>
> Steve Leyton
> Protection Design & Consulting
>
> The foregoing is the opinion of the writer alone, and does not necessarily
> represent the intent of the NFPA 14 Technical Committee, nor constitute a
> formal or informal interpretation of the standard.
>
>
>
> -----Original Message-----
> From: Timothy W Goins [mailto:[EMAIL PROTECTED]
> Sent: Tuesday, January 30, 2007 12:49 PM
> To: [email protected]
> Subject: RE: NFPA #14 and pressures
>
> Steve,
>
> In my opinion the 100 PSI reducer is still required for that reducer and
> it's proposed hose, if it is ever used. If I'm wrong please let me know
> and I'll paste it in my 14.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Steve
> Leyton
> Sent: Tuesday, January 30, 2007 2:36 PM
> To: [email protected]
> Subject: RE: NFPA #14 and pressures
>
>
> Timothy:
>
> Check out 7.3.4.1.2 (2007 ed.) and 7.3.4.1 (2003 ed.)
>
> Steve
>
>
> -----Original Message-----
> From: Timothy W Goins [mailto:[EMAIL PROTECTED]
> Sent: Tuesday, January 30, 2007 12:20 PM
> To: [email protected]
> Subject: RE: NFPA #14 and pressures
>
> The definition os a Clas III requires 1½" Hose statoins (hose included)
> and 2½" hose connections;
>
> 3.3.27.3 Class III System. A Class III standpipe system provides 38-mm
> (11⁄2-in.) hose stations to supply water for use by building occupants and
> 65-mm (21⁄2-in.) hose connections to supply a larger volume of water for
> use by fire departments and those trained in handling heavy fire streams.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Todd
> Williams - work
> Sent: Tuesday, January 30, 2007 2:12 PM
> To: [email protected]
> Subject: RE: NFPA #14 and pressures
>
>
> And even if they find one, would you trust an untrained person on the end
> of a hose with 100 psi discharge?
>
> At 03:02 PM 1/30/2007, you wrote:
>>One thing that does not make sense....where are these untrained people
>>going to get 1 1/2" hose?
>>
>>Paul J. Pinigis, P.E.
>>Chief Life Safety Engineer
>>
>>
>>
>>Must meet both criteria. The 1½" hose station is available for
>>untrained persons thus the pressure limit.
>>
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> 860-535-2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>


--------------------------------------------------------------------------------


> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to