Before you hired on I recall cutting such a deal with the Bird Dog
over the Smith Tower (47 stories for those of you from out of town)
when it was in receivership. Apartfrom the money thing if I recall the
real problem was not adding the pump but finding a place for an
emergency generator. the solution was to abandon the exterior Class I
that leaked like a sieve, change out the valves on the abandoned 6"
Class II, add an FDC, tempoarily adjust department tactics, and wait
to see what the future owners intended. The end result was everybody
being happy including the bankruptcy judge and the receiver. So once
again I'll reiterate Leyton's comment on another thread, "ALWAYS"
include the AHJ in your planning when your problem is a little to the
side of standard. Oh, and it works both ways. Yesterday I had an AHJ
with an old bowling alley that soehow got a sprinkler system approved
some years back that covered the floor area but ignored the
combustible space of ballroom proportions above the drop ceiling. He
was hoping I could conjure a code reference that allowed him to demand
a retrofit. I couldn't. Anybody got an idea?

On 1/31/07, R Richardson <[EMAIL PROTECTED]> wrote:
The way this issue works in Seattle is that if the renovation is
"significant" (subjective determination by building official, but
typically the building is being gutted to trigger this) then the project
is indeed subject to the requirement for an automatic standpipe, among
other things.  However, if the building is shorter than about 15 - 20
stories we typically waive the pump requirement (assuming sprinklers
don't need it) and accept manual standpipes.  However, we would probably
require the 4 in. standpie to be replaced with 6 in.

These projects always brings up all sorts of operational discussions
about the use of manual standpipes in the old unsprinklered high rise
buildings when using modern standpipe pressures against hose valves that
are not high pressure rated, nor behind PRV's.

Bottom line, meet with the AHJ.

Rich Richardson
Seattle Fire Department

>>> "art" <[EMAIL PROTECTED]> 01/31/07 6:43 AM >>>
We have a 100 ft high rise residential bldg. with major renovations.
There
are two existing 4" standpipes. The building will be retrofitted with
a
sprinkler system per NFPA 13. From NFPA 14 2003,can 5.4.1.3 be used to
not
require a fire pump to supply the standpipe 100 psi pressure since
this
existing 80 year old bldg is being sprinklered? Is the fire pump
required to
supply 750 gpm with 500 gpm at 100psi at the most remote standpipe?
Art Tiroly
ATCO Fire Protection


Roland Huggins wrote
excellent question.  I put my money on Steve's answer.   The NFPA
committees that I am on (or familiar with) are aggressively moving
away from encouraging occupants to use a hose (which correlates
nicely with OSHA requirements).

Roland

On Jan 30, 2007, at 1:02 PM, Steve Leyton wrote:

> I think that the sections I referenced are quite clear:
>
> "For Class III systems installed without hose, the water supply
> requirements shall be as specified for Class I systems."
>
> That would be ALL of the water supply design criteria, including
> both maximum and minimum pressures.
>
> Steve Leyton
> Protection Design & Consulting
>
> The foregoing is the opinion of the writer alone, and does not
> necessarily represent the intent of the NFPA 14 Technical
> Committee, nor constitute a formal or informal interpretation of
> the standard.
>
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to