Dewayne,

And Joe, please elaborate at your convenience as I know you have far
more background knowledge in this arena than I.

FM Data Sheet 2-2, Section 2.4.5.3.2 gives (what I believe to be) pretty
sufficient guidance in addressing your situation.

Specifically Item-4 

"If the obstructions below sprinklers is not continuous circular or
rectangular (such as a light) with a maximum dimension of 24" in.,
locate the sprinkler deflector at least 12" horizontally from the
nearest edge of the obstuction."

It seems to me a plumbing stack, rain leader, vertical exhaust duct etc.
could be treated the same, based on its size and per its obstruction
rules, whether it was vertical or horizontal.
It also seems to me a vertical obstruction affecting one sprinkler would
be less of a problem than the same obstruction placed horizontal
affecting more than one sprinkler if you place the sprinklers according
to the obstruction rules for the size of your obstruction and the
required distance of the sprinklers away from the obstruction. 

Yet we have specific guidance for the horizontal obstructions and not
the vertical ones. Hmmmm!

If the obstruction rules work for the horizontal obstructions, why would
they not also work for the vertical?
(I know the full development of the spray pattern and getting the
correct amount of water thru the fire plume to the base of the fire is
critical even for one sprinkler activating. It just seems to me that the
considerations would be much the same with the obstruction in either
plane.)

In closing, I would make the suggestion that spacing your sprinklers
from the vertical obstruction exactly as you would the horizontal would
give some level of confidence in maintaining the suppression mode of the
ESFR sprinklers.

We do not typically consider 6", 8", 10" vertical structural columns
(square, round, or otherwise) as obstructions. Of course we are usually
more than 2ft away from them :-)

Thanks,

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, February 07, 2007 9:01 AM
To: [email protected]
Subject: RE: ESFR AND VERTICAL OBSTRUCTIONS (NFPA 13 07ed)

So I take it that you have never installed ESFR sprinklers in a building
that included roof drains that run from the roof deck to the floor along
a column?     

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Wednesday, February 07, 2007 7:51 AM
To: [email protected]
Subject: Re: ESFR AND VERTICAL OBSTRUCTIONS (NFPA 13 07ed)

Dewayne,

If it is impractical, then don't install ESFR's. There are other
alternatives (e.g. in-rack sprinklers).  ESFRs are an option only if
their installation rules are met.

ESFR's are asked to do a lot more than any other sprinkler. As a result,
there is no margin for error when it comes to obstructions.  If there is
a single obstruction and the fire starts in the wrong spot, then failure
to suppress or control is a very real possibility. 

In the testing of ESFR sprinklers, the scenario of a fire starting
centered between two sprinklers with one of them obstructed resulted in
a barely controlled fire in a 30 ft. building (11 sprinklers operated)
and uncontrolled fire in a 40 ft. building.

Joe

Dewayne Martinez wrote:

>I am looking for some input from the forum on how you treat  a isolated

>vertical obstruction that restricts only one ESFR sprinkler head.  It 
>is both above and below the sprinkler.  Such as a round exhaust duct 
>from a unit heater below up through the deck or a plumber drain stack?

>An informal request to NFPA resulted in this response "Section
>8.12.5.2(5) allows sprinklers with special obstruction allowance shall 
>be installed in accordance with its listing. ESFR sprinklers have very 
>particular obstruction criteria, and interpolation, or modification of 
>obstruction rules is not allowed."  I have yet to find a ESFR sprinkler

>to address this issue, in the past I have followed the rules for 
>isolated obstructions below the sprinkler to provide guidance.  It 
>seems impractical to expect a storage building to be constructed 
>without any vertical obstructions.
> 
>Thanks,
>Dewayne Martinez
>Design Build Fire Protection
>[EMAIL PROTECTED]
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into "The Players Hall of Fame"
at The Great Games of Business
Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work"
Rated #1 in 2006
Large Business Category
by Orlando Business Journal