Agreed, 1000 gpm max for a sprinklered building.

Interestingly, (or maybe not), here in Seattle we have a local ammendment to 
NFPA that requires  at least one standpipe riser to have two 2 * in 
connections, but we don't even require the standpipe flow test at this point.

And as I read the 2007 NFPA 14 it too appears to require two 2 * in. 
connections.  Section 7.3.2 requires one connection at the top of each riser 
and 7.3.2.2 requires an additional connection at the hydraulic end of the 
system.  Oddly enough we do not even require more than one riser to have roof 
connections if the roof can be reached from the hose connection with 200 ft. of 
hose. 

A horizontal standpipe (think marinas) is typically designed for 1000 gpm in my 
experience.  And really that is not enough for a covered moorage type of fire 
in reality. 

Rich Richardson
Seattle Fire Department

The foregoing is the opinion of the writer alone, and does not necessarily 
represent the intent of the NFPA 14 Technical Committee, nor constitute a 
formal or informal interpretation of the standard.



>>> "Steve Leyton" <[EMAIL PROTECTED]> 02/07/07 8:13 AM >>>
Leyton just got into office - West Coast representin'!

Yes, I think it's intended that there be two FHV's available for testing at an 
approved location - ideally the most remote (usually top) of one or more 
standpipes.   Our practice is to furnish a two-way manifold at the top of all 
Class I standpipes, whether they are within a stair enclosure or free-standing 
on the roof.

WRT to the horizontal standpipe issue, I'm not sure and I think it's a great 
question.   On the one hand, the 1000 GPM cap on sprinklered buildings 
rightfully presumes that there will be a controlled fire scene and hose streams 
will be secondary and mop-up.   On the other hand, a horizontal standpipe is a 
completely different hydraulic model (at each floor) than if you took water 
from each of three FHV's that were independently supplied by two or three 
different risers.  

If you put a gun to my head, I'd say 1000 GPM cap on all sprinklered buildings, 
period.   Rich?

Steve Leyton
Protection Design & Consulting

The foregoing is the opinion of the writer alone, and does not necessarily 
represent the intent of the NFPA 14 Technical Committee, nor constitute a 
formal or informal interpretation of the standard.







-----Original Message-----
From: Ron Greenman [mailto:[EMAIL PROTECTED] 
Sent: Wednesday, February 07, 2007 7:28 AM
To: [email protected] 
Subject: Re: More NFPA 14 - 2003: Max Flow Horiz SP


Sounds like 750 to me if a single pipe and up to 1250 on any common
runs to multiple pipes. What's Leyton say?

On 2/7/07, Fletcher, Ron <[EMAIL PROTECTED]> wrote:
> In a fully sprinklered one story building what is the maximum flow for a
> single Class I horizontal standpipe system with more than three (30
> actual) connections? 750 gpm, 1000 gpm or 1250 gpm.
>
> 7.10.1.1.3 The minimum flow rate for additional standpipes shall be 946
> L/min (250 gpm) per standpipe, with the total not to exceed 4731 L/min
> (1250 gpm) or 3785 L/min (1000 gpm) for buildings sprinklered
> throughout.
>
> 7.10.1.2.2 Where a horizontal standpipe on a Class I and Class III
> system supplies three or more hose connections on any floor, hydraulic
> calculations and pipe sizes for each standpipe shall be based on
> providing 946 L/min (250 gpm) at the three hydraulically most remote
> hose connections on the standpipe and at the topmost outlet of each of
> the other standpipes at the minimum residual pressure required by
> Section 7.8
>
> 7.10.1.2.3 Common supply piping shall be calculated and sized to provide
> the required flow rate for all standpipes connected to such supply
> piping, with the total not to exceed 4731 L/min (1250 gpm).
>
> Ron Fletcher
> Aero Automatic Sprinkler
> Phoenix, AZ
>
> Aero Automatic Sprinkler
>
> PHoenix, AZ
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to