Well now, that may be though I would tend to be skeptical of that, I
usually mount the flow indicator high on the main riser anyway unless I am
using an AGF drain/test valve.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Friday, February 09, 2007 11:23 AM
To: [email protected]
Subject: Re: WATERFLOW SWITCHES

Since you can only use a vane switch in a wet pipe, and since there is no
sudden inrush I think the concern was more with being too close to the main
drain where there would be a sudden pressure drop that could pull the vane
backwards, either damaging the mechanism or pulling the vane off the shaft.

On 2/9/07, George Church <[EMAIL PROTECTED]> wrote:
> Sure you weren't thinking of a DPV or deluge?
>
> There's not a sudden inrush of water above a Alarm check.
>
> glc
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Bill 
> Minkel
> Sent: Thursday, February 08, 2007 6:39 PM
> To: [email protected]
> Subject: RE: WATERFLOW SWITCHES
>
> I have been told that when the flow switch is too close to an alarm 
> valve the sudden flow can damage or tear off the vane. Just what I was 
> told once, notta clue if it's a valid concern
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>


--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to