Well, there could be opening protection trade-offs, rating, building type,
and so on. I would think if the A-3 was incidental the architect would have
just called it a R2. He didn't so I am guessing the occupancies are not
incidential and 13 would be required. 

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Friday, February 09, 2007 2:35 PM
To: [email protected]
Subject: RE: Residential?

Well, it wouldn't have been for an area increase !
Seriously, I haven't even seen the full set of docs yet. 
But I doubt there were any, egress isn't stretched at all- 60' travel max.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Friday, February 09, 2007 4:08 PM
To: [email protected]
Subject: RE: Residential?

It will depend on the exceptions the architect took for trade-offs. Some of
the trade-offs allow you to install per 13 or 13R, some only allow 13. Did
he take any trade-offs? 

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Friday, February 09, 2007 2:06 PM
To: [email protected]
Subject: Residential?


We have a project in which the majority of the building is dorm rooms;
2nd flr (top) is all dorms, with a few more dorm rooms and a few classrooms
and offices on the first floor. Small basement is mechanical only. 
Entire building footprint is a whopping

The classrooms are for the use of the students that reside in the dorm; 
Offices for faculty that teach there. 

Overall concept is suburban campus college has this building in the city for
students to study government and urban life. So the non-residential areas
are incidental to the residential nature of the building.

The Architect has deemed the building A3 for the first floor, R2 on 2nd
floor. Naturally the one hour separation is at the first floor ceiling.

If this sounds a little strange, at least it's not #13TR, elderly housing
over tire storage:)  This IS located in a locale where 13d tank/pumps feed 3
story office buildings, with poly tanks located in restaurant storage area,
and CPVC in OH2. Sure, that will make the judge understand ?

Anyway, would % of use and other uses being for the occupants make this look
#13R to any of you?

George Church
Rowe Sprinkler

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to