A 10.4.1 clearly states "Recommended Depths". Also, at the beginning of Annex A you will find this text:
"Annex A is not a part of the requirements of this NFPA document but is included for informational purposes only. This annex contains explanatory material, numbered to correspond with the applicable text paragraphs." Tony Liddic, CET Fire Sprinkler Designer AEC Fire & Security 400 Fame Rd. West Carrollton, OH 45449 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Randy Knutson Sent: Thursday, February 15, 2007 5:33 PM To: [email protected] Subject: Depth of Cover I don't know if this is getting posted. If this shows up several times forgive me. If I know what my frost depth is locally do I have follow Figure A 10.4.1 in NFPA 13? Our local frost depth is 24". Per NFPA 13:10.4.2 "The top of pipe shall be buried not less than 1 ft. below the frost line for locality." That gives me a 36" depth of bury from top of pipe. The local AHJ saying that it has to have 4'-6" of cover because that is what is shown in figure A 10.4.1. I'm arguing that this is a recommendation to be used if you don't have your frost depth for your locality. He says the Figure A 10.4.1 gives the required depth. Please help. Thank you, Randy Knutson Shilo Automatic Sprinkler, Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum