We sprinklered one similar to your due to lack of fire separation.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, March 02, 2007 8:32 AM
To: [email protected]
Subject: RE: Porte cocheres

Ruling we had was that combustible then sprinkle.  If not combustible we
did not have to sprinkle as long as the cars were there only temporarily
for pickup or drop off, not long term parking.

If yours is detached and combustible he could be citing separation
issues as listed in the IBC that can dictate the need for sprinklers in
the PC.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rod
DiBona
Sent: Thursday, March 01, 2007 6:20 PM
To: [email protected]
Subject: Porte cocheres

Is there any clear cut building code or nfpa standard that addresses
sprinklering porte cocheres?(normally the drive under entrance for
motels) I had the understanding that if they are attached and
combustible they needed to be covered but if they weren't BOTH that they
didn't. I have an "unattached" combustible porte cochere at a motel
where the fire marshal has asked us to sprinkler it from the dry system
in the attic. Thank you for your input.

Rod DiBona
Rapid Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to