David,
Mild, Hot or Nuclear aside, it don't think that salsa would meet the
same standard as juice or soda. I believe (and I think Joe could help
me out here), part of that comes from the fact the when a bottle of
soda (or whatever liquid) breaks, you would get a flood of liquid
that could inhibit the spread of the fire. Most salsa worth anything
would flow that much, so you wouldn't get the same effect.
Todd
At 02:37 PM 3/6/2007, you wrote:
Dear Forum,
According to NFPA 1 (2003) 13.3.2.23.1 a sprinkler system is required for
high-piled storage of combustibles over 2500 sq. ft., and A13.3.2.23 states
that for this purpose combustibles include non-combustibles packaged in
combustible materials.
According to NFPA 13 (2002) Table A.5.6.3 glass jars filled with
non-combustible liquids is a Class I commodity. 5.6.3.1, states that Class I
shall be defined as non-combustible.
Question I have is: What would salsa in glass jars packaged in cardboard
boxes (cases) stored over 12 ft. in racks be classified as?
It appears to me that NFPA 1 says to sprinkle the building, and then NFPA 13
says its noncombustible storage for the purpose of determining rack storage
protection. Is this a fair statement?
David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum