more worried about it NOT staying in its intended orientation.
Joe - Did you guys see any systems where sprigs and rotated?
Roland
On Mar 8, 2007, at 7:01 PM, Joe Hankins wrote:
There was nothing to suggest water hammer. Water hammer resulting
from a pump start is unlikely in sprinkler system piping. Even if
there is a water hammer problem, it's something you want to know
because it's easy to fiz.When you do see water hammer from a fire
pump, it usually happens in underground.
Also, starting fire pumps with the discharge valve open is by far
the most common way weekly runs are made. I've seen many sprinkler
systems that have held up to weekly pump starts for more than 30
years without incident.
If you truly beleive that a sprinkler system can be blown apart by
a fire pump, you have a very low opinion of the quality of
sprinkler installations!
Joe