Since this is a test:

1) The meter will have no effect on the operation of the 13D system if you install it per NFPA 13D, 2007 Figure A.6.2(a) or (b)

or

2) There are no 5/8" meters that will not screw you over bad for pressure and flow.The only possible hope is you have no rooms with more than 1 head, and the largest room is no more than 12x12. The 3/4" meters may allow the Gpm you need but the pressure drop will be excessive. Get the water purveyor to allow you to by-pass the meter or supply a 1" full port (flow) meter for 13D systems.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Chris Brown" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, March 09, 2007 8:18 AM
Subject: Pandora's Box


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to