Okay, since Roland mentions Dallas water dept/utilities (DWU), I thought I'd contribute to this discussion. Contrary to what Roland has inferred, DWU actually is very understanding and has tried to address the reliability of the domestic meters during high flow (fire) conditions.
Prior to about mid-2003, DWU allowed a minimum 2-in turbine meter for 13D or 13R applications where the total flow rate (domestic & fire) was less than 150-gpm. Due to cost considerations by the builders, DWU changed their policy to allow 1-in minimum "multi-jet" meters for 13D applications only. DWU claims that the older "positive displacement" meters are more likely to fail closed at higher flow rates than the newer "multi-jet" meters. Don't ask me what the differences are cause I don't know the answer. Anyway, DWU guidelines are: 5/8-in has max flow of 30-gpm (not allowed for 13D applications) 1-in has 50-gpm 1 ½-in has 100-gpm 2-in has 150-gpm My job is to insure that whatever meter is installed (1-in, 1 ½-in, or 2-inch) is adequate to provide the required fire sprinkler and domestic flow at the calculated pressure. rick matsuda city of dallas, building inspection dept. >>> [EMAIL PROTECTED] 03/09/07 10:31AM >>> I know the Dallas water dept will not allow small standard water meters (displacement types I think) to be used on a residential sprinkler system. They say these unit will not operate RELIABLY at the higher flow presented by the sprinkler system. I believe they require a minimum 1 -1/2 inch meter. They never defined what aspect of reliable operation was the concern. It could be the ability to accurately read the amount of water. Roland _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum