Okay, since Roland mentions Dallas water dept/utilities (DWU), I thought I'd 
contribute to this discussion. Contrary to what Roland has inferred, DWU 
actually is very understanding and has tried to address the reliability of the 
domestic meters during high flow (fire) conditions. 

Prior to about mid-2003, DWU allowed a minimum 2-in turbine meter for 13D or 
13R applications where the total flow rate (domestic & fire) was less than 
150-gpm. Due to cost considerations by the builders, DWU changed their policy 
to allow 1-in minimum "multi-jet" meters for 13D applications only.

DWU claims that the older "positive displacement" meters are more likely to 
fail closed at higher flow rates than the newer "multi-jet" meters. Don't ask 
me what the differences are cause I don't know the answer.

Anyway, DWU guidelines are:
5/8-in has max flow of 30-gpm (not allowed for 13D applications)
1-in has 50-gpm
1 ½-in has 100-gpm
2-in has 150-gpm

My job is to insure that whatever meter  is installed (1-in, 1 ½-in, or 2-inch) 
is adequate to provide the required fire sprinkler and domestic flow at the 
calculated pressure.

rick matsuda
city of dallas, building inspection dept.

>>> [EMAIL PROTECTED] 03/09/07 10:31AM >>>
I know the Dallas water dept will not allow small standard water  
meters (displacement types I think) to be used on a residential  
sprinkler system.  They say these unit will not operate RELIABLY at  
the higher flow presented by the sprinkler system.  I believe they  
require a minimum 1 -1/2 inch meter.  They never defined what aspect  
of reliable operation was the concern.  It could be the ability to  
accurately read the amount of water.

Roland