If your using a fitting attachment similar to the TOLCO Fig. 909 or 910 and your brace angle is less than 60 deg. from horizontal the load is all shear. From 60 deg. on down to 90 (vertical) the load becomes increasingly Tension. You'll find it very beneficial to keep your hangers between 30 to 45 deg. from horizontal.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Bob Knight" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, March 09, 2007 1:13 PM
Subject: Sway Bracing Fasteners


When sizing the size of fasteners for the attachment of sway bracing to
post-tension slabs, do I need to be concerned with tension load or shear
load?  The reason I ask is that we will be using HILTI HDI-P 3/8" concrete
inserts. It has an allowable load under tension of 380 lbs and an allowable
load of 600 lbs under shear stress.  I may be making the wrong assumption,
that's why I'm asking, but with sway bracing are we concerned with tension
or shear? I'm thinking shear. The lateral braces can be on 40' centers at
only 271 lbs per brace, but the longitudinal braces, at 542 lbs per brace,
need to have the distance between them shortened if tension is my concern.
Thanks for your help.

Bob Knight, CET
(208) 495-2057
[EMAIL PROTECTED]
www.firebyknight.com


--
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007
10:58 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to