Does anyone know how much pressure would it take to push 35 gpm through a 3/4" meter?
Thanks - Garth ----- Original Message ----- From: "PCE" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Friday, March 09, 2007 2:01 PM Subject: Re: Pandora's Box Chris, Badger makes a meter, model M40, which is 3/4 x 3/4, and their chart shows that it can accept flows of up to 35 gpm. And, at that flow, it has a pressure loss of around 6.5 to 7.0 psi. I would think that would certainly be sufficient to not impact the design of a residential system at the same level as the chart losses shown in NFPA-13D. Out here, the AHJ's are starting to require the designers [sue me if you don't like that word] to submit the data on the meter along with the calculations and plans. Just one more item to check prior to submittal. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website Chris Brown wrote: > Thank you for the information and now we have another manufacturer a > meter of with the same results as described in my last email, a 5/8 inch > or 3/4 inch will not meet the flow requirements of a lot of the NFPA 13D > and NFPA 13R systems. IF as the AHJ, designer or installer of such > systems you should be thinking pretty hard right now. > > > Thank you, > > Chris Brown > Fire Protection Designer, Poole Fire Protection > Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600 Fax: > 913.829.8690 > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Kathryn > Tyler > Sent: Friday, March 09, 2007 11:40 AM > To: [email protected] > Subject: RE: Pandora's Box > > This is the water meter we use here a lot. > http://www.badgermeter.com/pdf/recdisk/tech/rd-t-34.pdf > > http://www.vikinggroupinc.com/databook/sprinklers/residential/103105.pdf > is an example of a concealed head that could work with up to 16x16 > spacing (flat ceilings only though - if on sloped clgs, the press. > requirement goes way up) There are others that will work, but this is an > example. Generally, it is tough to go more than 16x16 spacing with a > 3/4" meter, unless the run of copper between the tap and meter is very > short, the water pressure is very high. (Don't forget the loss through > the pipe between the tap and meter must be included in the calcs) Many > have requested for only 1" meters to be installed now, which is a lot > more expensive. > Kathryn > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of PCE > Sent: Friday, March 09, 2007 8:48 AM > To: [email protected] > Subject: Re: Pandora's Box > > Chris, > > They would have the same effect that any valve or fitting would have on > the ability of a sprinkler system to function properly. The loss in > pressure due to friction at various flows through the meters is required > to be accounted for in the hydraulic calculations. Interestingly > enough, NFPA-13D tells us that the actual chart loss from the meter > manufacturer should be reviewed during the calculation process. If the > chart loss is lower than those figures in the table in 13D it may be > used, however the standard also says that if the chart loss from the > manufacturer is greater than those shown in the table that the higher > value MUST be used. > > Out here we see hundreds of residential sprinklers systems every month, > and for the most part they utilize 1" meters. With a 13 gpm demand per > sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31 > gpm exceeds the values shown in 13D as acceptable for a 5/8", and is > right on the line at the maximum allowed for a 3/4". > > There has been much shouting regarding the issue of meter size out here, > and most of it accompanied by vague suggestions of dire consequences and > thousands of dollars needlessly wasted if one position or another isn't > followed. > > What is your take on the issues involved? > > PARSLEY CONSULTING > > Ken Wagoner, SET > > 760.745.6181 voice > > 760.745.0537 fax > > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail > > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website > > > > > Chris Brown wrote: > >> Question to the forum: >> What effect does a 5/8 inch or 3/4 inch water meter have on fire >> sprinkler >> > system installed in an NFPA 13D or NFPA 13R system. The issue is one of > the maximum continuous flow thru the meter and its effect on the ability > of the fire sprinkler system to operate as intended. I respectfully > request, Please research and answer after you have visited with the > water meter manufacturer's and or water departments as I have already > done. Keep in mind that a single residential sprinkler has a minimum of > some where between 19 and 25 gpm requirements and that most dwellings > have two sprinklers flowing in the hydraulically remote area. > >> >> This will be fun for a Friday:) >> >> Thank you, >> >> Chris Brown >> Fire Protection Designer >> Please note our new company name, e-mail address and web site. >> >> >> >> innovative leader $B"%(J trusted partner >> >> 19910 West 161st Street >> Olathe, KS 66062 >> Office: 913.829.8650 >> >> Direct: >> Cell: >> Fax: >> >> 913.747.2056 >> 913.208.3600 >> 913.829.8690 >> >> www.poolefire.com <http://www.poolefire.com/> Office Map >> <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&c >> ity=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%2 >> 0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%20 >> US&cid=lfmaplink2&name=> >> >> This e-mail, and any files transmitted with it, are confidential and >> > intended solely for the use of the individual or entity to which they > are addressed. If you have received this e-mail in error, please notify > [EMAIL PROTECTED] > >> >> >> >> ---------------------------------------------------------------------- >> -- >> >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> ---------------------------------------------------------------------- >> -- >> >> No virus found in this incoming message. >> Checked by AVG Free Edition. >> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: >> 3/8/2007 10:58 AM >> >> > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum