Could be a lot. You'd have to get the information from the manufacturer. They can be stingy about giving it out, but they do have it. I recently went through this drill on a 1-1/2" meter.

BTW, if there is someone living in South Florida out there, would you please e-mail me privately. Thanks.


At 06:11 PM 3/9/2007, you wrote:
Does anyone know how much pressure would it take to push 35 gpm through a
3/4" meter?

Thanks -
Garth
----- Original Message -----
From: "PCE" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, March 09, 2007 2:01 PM
Subject: Re: Pandora's Box


Chris,

Badger makes a meter, model M40, which is 3/4 x 3/4, and their chart
shows that it can accept flows of up to 35 gpm.  And, at that flow, it
has a pressure loss of around 6.5 to 7.0 psi.  I would think that would
certainly be sufficient to not impact the design of a residential system
at the same level as the chart losses shown in NFPA-13D.

Out here, the AHJ's are starting to require the designers [sue me if you
don't like that word] to submit the data on the meter along with the
calculations and plans.

Just one more item to check prior to submittal.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Chris Brown wrote:
> Thank you for the information and now we have another manufacturer a
> meter of with the same results as described in my last email, a 5/8 inch
> or 3/4 inch will not meet the flow requirements of a lot of the NFPA 13D
> and NFPA 13R systems. IF as the AHJ, designer or installer of such
> systems you should be thinking pretty hard right now.
>
>
> Thank you,
>
> Chris Brown
> Fire Protection Designer, Poole Fire Protection
> Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600   Fax:
> 913.829.8690
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Kathryn
> Tyler
> Sent: Friday, March 09, 2007 11:40 AM
> To: [email protected]
> Subject: RE: Pandora's Box
>
> This is the water meter we use here a lot.
> http://www.badgermeter.com/pdf/recdisk/tech/rd-t-34.pdf
>
> http://www.vikinggroupinc.com/databook/sprinklers/residential/103105.pdf
> is an example of a concealed head that could work with up to 16x16
> spacing (flat ceilings only though - if on sloped clgs, the press.
> requirement goes way up) There are others that will work, but this is an
> example. Generally, it is tough to go more than 16x16 spacing with a
> 3/4" meter, unless the run of copper between the tap and meter is very
> short, the water pressure is very high. (Don't forget the loss through
> the pipe between the tap and meter must be included in the calcs) Many
> have requested for only 1" meters to be installed now, which is a lot
> more expensive.
> Kathryn
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of PCE
> Sent: Friday, March 09, 2007 8:48 AM
> To: [email protected]
> Subject: Re: Pandora's Box
>
> Chris,
>
> They would have the same effect that any valve or fitting would have on
> the ability of a sprinkler system to function properly.  The loss in
> pressure due to friction at various flows through the meters is required
> to be accounted for in the hydraulic calculations.  Interestingly
> enough, NFPA-13D tells us that the actual chart loss from the meter
> manufacturer should be reviewed during the calculation process.  If the
> chart loss is lower than those figures in the table in 13D it may be
> used, however the standard also says that if the chart loss from the
> manufacturer is greater than those shown in the table that the higher
> value MUST be used.
>
> Out here we see hundreds of residential sprinklers systems every month,
> and for the most part they utilize 1" meters.  With a 13 gpm demand per
> sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31
> gpm exceeds the values shown in 13D as acceptable for a 5/8", and is
> right on the line at the maximum allowed for a 3/4".
>
> There has been much shouting regarding the issue of meter size out here,
> and most of it accompanied by vague suggestions of dire consequences and
> thousands of dollars needlessly wasted if one position or another isn't
> followed.
>
> What is your take on the issues involved?
>
> PARSLEY CONSULTING
>
> Ken Wagoner, SET
>
> 760.745.6181 voice
>
> 760.745.0537 fax
>
> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
>
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>
>
>
>
> Chris Brown wrote:
>
>> Question to the forum:
>> What effect does a 5/8 inch or 3/4 inch water meter have on fire
>> sprinkler
>>
> system installed in an NFPA 13D or NFPA 13R system. The issue is one of
> the maximum continuous flow thru the meter and its effect on the ability
> of the fire sprinkler system to operate as intended. I respectfully
> request, Please research and answer after you have visited with the
> water meter manufacturer's and or water departments as I have already
> done. Keep in mind that a single residential sprinkler has a minimum of
> some where between 19 and 25 gpm requirements and that most dwellings
> have two sprinklers flowing in the hydraulically remote area.
>
>>
>> This will be fun for a Friday:)
>>
>> Thank you,
>>
>> Chris Brown
>> Fire Protection Designer
>> Please note our new company name, e-mail address and web site.
>>
>>
>>
>> innovative leader    $B"%(J     trusted partner
>>
>> 19910 West 161st Street
>> Olathe, KS  66062
>> Office:  913.829.8650
>>
>> Direct:
>> Cell:
>> Fax:
>>
>> 913.747.2056
>> 913.208.3600
>> 913.829.8690
>>
>> www.poolefire.com <http://www.poolefire.com/> Office Map
>> <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St&c>> ity=Olathe&state=KS&zipcode=66062-2700&country=US&title=%3cb%3e19910%2
>> 0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-2700,%20%20
>> US&cid=lfmaplink2&name=>
>>
>> This e-mail, and any files transmitted with it, are confidential and
>>
> intended solely for the use of the individual or entity to which they
> are addressed.  If you have received this e-mail in error, please notify
> [EMAIL PROTECTED]
>
>>
>>
>>
>> ----------------------------------------------------------------------
>> --
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> ----------------------------------------------------------------------
>> --
>>
>> No virus found in this incoming message.
>> Checked by AVG Free Edition.
>> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date:
>> 3/8/2007 10:58 AM
>>
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to