Greg,

It depends on the type of wall.

For dry wall construction such as gypsum board normally the wall lining
manufacturer will have had wall assemblies tested to ASTM E119 and publish
the results in their literature.

Concrete walls - For straight heat transfer SFPE Handbook of Fire Protection
Engineering 3rd edition Fig 4-10.6 gives the fire endurance for various slab
thicknesses and concrete types to meet ASTM E119 (There are probably other
sources on the internet that would aslo provide this same data). To consider
stability both during and after a fire requires a structural engineer to
carry out some calculations. 

Regards,

Michael James
Fire Safety Engineer
Pacific Consultants
Auckland
NZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Sunday, 11 March 2007 11:40 a.m.
To: [email protected]
Subject: RE: RECOMMANDATIONS FOR TRAINING

Where can I find the fire resistance rating of a wall?