This is an old thread, but I'm working on two projects, a six storey and 9
storey with fire pumps and it got me thinking (not an easy feat). Most
times, the problem is not when you have a large flow through the sprinklers
or hose stations. It is when the flow is small or at churn pressure. When
the flow is large, the pressure has dropped down below 175 psi. When the
flow is small you don't need the extra pressure. So if you install a
pressure relief valve set at say 160 psi, you shouldn't need the XH pipe,
fittings and pressure reducing valves. I might be wrong, but I'm thinking
the pressure relief valve must be costing less than a pressure reducing
valve. Any thoughts?

Tony 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- work
Sent: February 7, 2007 7:22 AM
To: [email protected]
Subject: pump tricks

I seem to be running into several situations lately where there is a 
very fine balancing act between meeting the 100 psi at the top outlet 
of the standpipe and not exceeding 175 psi at the base of the riser. 
(6 story hotels are a good example) Does anybody have any good ideas 
they'd care to share on making these work? I'd like to limit the use 
of extra-heavy pipe and fitting (especially larger sizes) and PRVs. I 
have several tricks up my sleeve, but I'm running out of sleeves.

Todd

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to