5.18.1.3 Where an electric variable speed pressure limiting control driver
is installed, and the maximum total discharge head adjusted for elevation
with the pump operating at shutoff and rated speed exceeds the pressure
rating of the system components, a pressure relief valve shall be installed.


 

We do not use Relief valves any more. We rely on the proper rated fittings
and Pressure Reducing Valves. The relief valves we have seen do not operate
quickly enough to save the system from being exposed to higher pressure and
they discharge so much water that they destroy property.

 

Plus we have never understood this section because it defeats the purpose of
the relief valve in regards to the rating of the fittings. This actually
traps the pressure in the system if the relief valve is slow in opening.

 

5.18.3 Location. The relief valve shall be located between the pump and the
pump discharge check valve and shall be so attached that it can be readily
removed for repairs without disturbing the piping.

 

Greg

 

Living Water Fire Protection, LLC

1160 McKenzie Road

Cantonment, FL 32533

850-937-1850

Fax: 850-937-1852

 

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby
McCullough
Sent: Wednesday, March 14, 2007 8:18 AM
To: [email protected]
Subject: RE: pump tricks

 

Greg:

 

Here in Georgia we adopted NFPA 20, 2003 two months ago and we may very

well adopt 2007 later this year.  I'm trying to figure out the

application of the main relief valve.

 

(2007) 5.18.1.2* Pressure relief valves shall be used only where

specifically permitted by this standard.

 

Does the standard specifically allow the use of a main pressure relief

valve anywhere except for use with a diesel pump and/or in combination

with a variable speed drive?

 

Bobby

 

 

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of Greg

McGahan

Sent: Wednesday, March 14, 2007 8:28 AM

To: [email protected]

Subject: RE: pump tricks

 

It is not allowed to eliminate pressure reducing valves on any pump. In

the

old days we did it but now we are required to provide PRV's anywhere the

fittings and sprinklers working pressure is less than the greatest

expected

pressure on the components (churn + static - elevation loss).

 

5.7.6.1 The net pump shutoff (churn) pressure plus the maximum static

suction pressure, adjusted for elevation, shall not exceed the pressure

for

which the system components are rated. 

 

5.7.6.2* Pressure relief valves and pressure regulating devices in the

fire

pump installation shall not be used as a means to meet the requirements

of

5.7.6.1.

 

Greg

 

Living Water Fire Protection, LLC

1160 McKenzie Road

Cantonment, FL 32533

850-937-1850

Fax: 850-937-1852

 

 

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of Bobby

McCullough

Sent: Wednesday, March 14, 2007 7:14 AM

To: [email protected]

Subject: RE: pump tricks

 

Tony:

 

I believe NFPA 20 2003 and 2007 limit the use of a main pressure relief

valve for use with a diesel pump and/or in combination with a variable

speed drive.  I don't believe the relief valve is allowed with an

electric pump just to chop off the high end of the pressure curve.

 

Bobby McCullough

 

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva

Sent: Wednesday, March 14, 2007 1:37 AM

To: [email protected]

Subject: RE: pump tricks

 

This is an old thread, but I'm working on two projects, a six storey and

9

storey with fire pumps and it got me thinking (not an easy feat). Most

times, the problem is not when you have a large flow through the

sprinklers

or hose stations. It is when the flow is small or at churn pressure.

When

the flow is large, the pressure has dropped down below 175 psi. When the

flow is small you don't need the extra pressure. So if you install a

pressure relief valve set at say 160 psi, you shouldn't need the XH

pipe,

fittings and pressure reducing valves. I might be wrong, but I'm

thinking

the pressure relief valve must be costing less than a pressure reducing

valve. Any thoughts?

 

Tony 

 

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of Todd

Williams

- work

Sent: February 7, 2007 7:22 AM

To: [email protected]

Subject: pump tricks

 

I seem to be running into several situations lately where there is a 

very fine balancing act between meeting the 100 psi at the top outlet 

of the standpipe and not exceeding 175 psi at the base of the riser. 

(6 story hotels are a good example) Does anybody have any good ideas 

they'd care to share on making these work? I'd like to limit the use 

of extra-heavy pipe and fitting (especially larger sizes) and PRVs. I 

have several tricks up my sleeve, but I'm running out of sleeves.

 

Todd

 

Todd G. Williams, PE

Fire Protection Design/Consulting

Stonington, Connecticut

860-535-2080

www.fpdc.com 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to