Yes, the insurance underwriters can add their requirements, but the AHJ
cannot.  The AHJ is tasked with enforcing the adopted codes, not
inventing new ones or adding his/her personal preferences.  The code
does not demand a pressure cushion, neither can the AHJ.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, March 16, 2007 9:41 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

Also, some insurance underwriters and AHJ's have requirements relating
to particular required safety factors in the calcs.  Don't forget to
check with them as well.   


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, March 16, 2007 9:31 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

If you can achieve 10% without spending your client's money (or your
own) great, but it is not necessary.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Friday, March 16, 2007 9:29 AM
To: [email protected]
Subject: RE: Minimum Supply Pressure

10% is what we go by, based on your numbers your only at around 2% :(

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, March 16, 2007 10:19 AM
To: [email protected]
Subject: Mininum Supply Pressure

Hello All,

Let me be the one to start things today.

What is the minimum safety pressure allowed ? I have looked in 13 and
did not find it....  I have a situation where the safety pressure is
0.913 psi.

Basis is:
 Hose 250
 Static 67.00
 Residual 38.00 @ 920.00
 Available 40.128 @ demand of 882.87
 Requires 39.215 psi
 Leaving a safety of 0.913 psi
 

--
Best regards,
 Charles                          mailto:[EMAIL PROTECTED]
Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to