No one in the Pittsburgh Office provided that information, it came from
F&EC 1 training in Massachusetts.  Still have it in my notes.    

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Friday, March 16, 2007 2:26 PM
To: [email protected]
Subject: Re: Minimum Supply Pressure

Paul,

While I can't say no one in the Pittsburgh Office told you that, I can 
tell you that it did not come from any data that FM had then or has 
now.  I know because I tried to squeeze some conclusion like that out of

the loss data base, but couldn't do it and still maintain any semblance 
of statistical rigor.

Joe

Paul Pinigis wrote:

>Those statistics were given to me by Factory Mutual when I worked for
>their Pittsburgh office.  I have never heard the one about no
>multi-death fires in sprinkered buildings, so I can't help you there.

>
>Paul J. Pinigis, P.E.
>Chief Life Safety Engineer
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Joe
>Hankins
>Sent: Friday, March 16, 2007 11:56 AM
>To: [email protected]
>Subject: Re: Minimum Supply Pressure
>
>Paul,
>
>Could you pleas provide the source of your statistics?  I've heard them

>quoted many, many times, but never found anyone who could point to the 
>actual data behind them.  There is another one going around for years 
>that says there has never been a multiple-death fire in a sprinklered 
>building. That one is definitely not true.
>
>Before we start talking about "overkill" in sprinkler designs we need
to
>
>recognize that some current standards have large safety factors, some 
>have none, and most have unknown safety factors. 
>
>The idea that there is a huge difference between a 5-sprinkler fire and

>a 15- or 30-sprinkler fire seems logical on the surface, but if you
know
>
>how sprinklers operate, you know they operate in rings. The heat that 
>operates sprinklers spreads in a circle from the fire origin.  For 
>symetrically-spaced sprinkler system where the fire starts centered 
>among 4 sprinklers,  there are 4 sprinklers in the first ring around 
>ignition,  so there is virtually no difference between a 1-sprinkler 
>fire and a 4-sprinkler fire. If those sprinklers don't control the
fire,
>
>then any (and all) of the 12 sprinklers in the next ring can operate, 
>meaning that there is very little difference betwen a 5-sprinkler fire 
>and a 16 sprinkler fire.  If you get into the next ring, then the
number
>
>is 36 sprinklers.  So, the 1-ring "safety factor" between 4 and 16 
>sprinklers is the same as the 1-ring safety factor between 16 and 36 
>sprinklers. A 1-ring "safety factor" is not overkill in my book!
>
>Finally, the "cushion" sometimes applied to a water supply is not a 
>safety factor. In addition to accounting for seasonal, weekly, daily, 
>and hourly fluctuations, it is a recognition that water supplies 
>invariably deteriorate and an attempt to avoid the large cost of 
>upgrading the system or water supply when it does. I'll agree that 
>adding a cushion to a fire pump supply dedicated solely to a fire 
>protection system is not necessary, because the pump supply stays the 
>same unless there is a problem with the pump, which must be fixed 
>immediately.
>
>Joe
>
>Paul Pinigis wrote:
>
>  
>
>>My point is that there are already so many factors of safety built
into
>>the design of a system that one more is overkill upon overkill.  95%
of
>>fires are controlled with one sprinkler operating, 98% of fires are
>>controlled with five or less operating, yet we calculate 1,500 square
>>feet (or 3,000 square feet for military projects), them we
overestimate
>>the friction loss in pipe and fittings, underestimate the water
supply,
>>them worry about adding an additional cushion. 
>>
>>Please, no "what about the other 2%" comments.  
>>
>>Paul J. Pinigis, P.E.
>>Chief Life Safety Engineer
>>
>>-----Original Message-----
>>From: [EMAIL PROTECTED]
>>[mailto:[EMAIL PROTECTED] On Behalf Of George
>>Church
>>Sent: Friday, March 16, 2007 9:56 AM
>>To: [email protected]
>>Subject: RE: Minimum Supply Pressure
>>
>>Well, there ARE a few more considerations.
>>Was the supply adjusted for lowest tank gradient? 
>>What confidence level do you have in the accuracy of the test data ?
>>What confidence level do you have that NO additional 90's will be
>>    
>>
>added?
>  
>
>>What is the Owner's tolerance for risk?
>>
>>NFPA #13 does NOT require a cushion. Good trade practice, flexibility
>>    
>>
>of
>  
>
>>installation changes, common sense, and protection of your boss's
>>retirement
>>assets require a cushion of some sort. So may the various AHJs you
>>    
>>
>face-
>  
>
>>water co, fire and code officials, insurance carrier, etc.
>>
>>So you could be right and fine with .0001 cushion- but in so doing,
you
>>may
>>find yourself in a box scratching for 2.7 PSi in a .0001 margin when a
>>duct
>>doesn't go in as planned, some cable bracing is discovered, ANYTHING. 
>>
>>We deal with a water company that applies a .8 coefficient to all
>>hydrant
>>test. If your test was from a .7 hydrant, the supply is overstated and
>>your
>>system, upon correction, would be 5 or 6 PSI shy. Or if the tank level
>>was
>>3' above lowest tank gradient, your system won't work in August.
>>
>>Or 4 heads could control the fire and everyone smiles. We just don't
>>know
>>EVERYTHING and we can't look into the future. I have trouble sleeping
>>when
>>we don't have 10%, and prefer 15 PSI+ on prelims on bid day. We just
>>analyzed a new site for a customer wanting to use K25s without a pump-
>>would
>>you tell him, based on 3.6 PSI cushion and ignorant of bar joist
>>spacing,
>>that it would? We're proceeding with a pump, and if things turn out
>>better
>>we can omit it, give him a credit for the pump, take some back with
the
>>$^
>>of k25's, but at least the money's in the job to start with. 
>>
>>When I was assetless and worked for others, I'd consider installing
>>    
>>
>what
>  
>
>>you
>>have. Now, not without everyone involved knowing it, and not if I was
>>    
>>
>on
>  
>
>>the
>>hook for the pump or larger piping replacement, or dual feed mains, or
>>whatever was needed to fix whatever changed and bumped us up. Imagine
>>going
>>to an owner with a $50,000 adder and explaining it with "we had to add
>>    
>>
>a
>  
>
>>6"
>>90 at the top of the riser." Not a situation I'd look forward to !
>>
>>glc
>>
>>-----Original Message-----
>>From: [EMAIL PROTECTED]
>>[mailto:[EMAIL PROTECTED] On Behalf Of Paul
>>Pinigis
>>Sent: Friday, March 16, 2007 9:31 AM
>>To: [email protected]
>>Subject: RE: Minimum Supply Pressure
>>
>>If you can achieve 10% without spending your client's money (or your
>>own) great, but it is not necessary.  
>>
>>Paul J. Pinigis, P.E.
>>Chief Life Safety Engineer
>>
>>-----Original Message-----
>>From: [EMAIL PROTECTED]
>>[mailto:[EMAIL PROTECTED] On Behalf Of Brian
>>Harris
>>Sent: Friday, March 16, 2007 9:29 AM
>>To: [email protected]
>>Subject: RE: Minimum Supply Pressure
>>
>>10% is what we go by, based on your numbers your only at around 2% :(
>>
>>          Regards,
>>             Brian Harris
>>First Defense Fire Protection
>>       Design Engineer
>>  [EMAIL PROTECTED]
>>          704.948.3506 phone
>>          704.948.3507 fax
>>
>>
>>-----Original Message-----
>>From: [EMAIL PROTECTED]
>>[mailto:[EMAIL PROTECTED] On Behalf Of Charles
>>Thurston
>>Sent: Friday, March 16, 2007 10:19 AM
>>To: [email protected]
>>Subject: Mininum Supply Pressure
>>
>>Hello All,
>>
>>Let me be the one to start things today.
>>
>>What is the minimum safety pressure allowed ? I have looked in 13 and
>>did not find it....  I have a situation where the safety pressure is
>>0.913 psi.
>>
>>Basis is:
>>Hose 250
>>Static 67.00
>>Residual 38.00 @ 920.00
>>Available 40.128 @ demand of 882.87
>>Requires 39.215 psi
>>Leaving a safety of 0.913 psi
>>
>>
>> 
>>
>>    
>>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to