David,
 
What is CMS? I didn't know of any situation where internal protection is
required in furniture but if there is a case I want to know about it.
 
Thanks,
 
Rod DiBona
Rapid Fire Protection

________________________________

From: [EMAIL PROTECTED] on behalf of David Autry
Sent: Fri 3/16/2007 9:41 AM
To: [email protected]
Subject: RE: Sprinklers in office closets



Unless, of course, you're doing a nursing home where CMS is involved.

>>>>> Furniture does not require internal sprinkler protection.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis
Sent: Friday, March 16, 2007 10:38 AM
To: [email protected]
Subject: RE: Sprinklers in office closets

Furniture does not require internal sprinkler protection.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thomas
Reinhardt
Sent: Friday, March 16, 2007 11:31 AM
To: [email protected]
Subject: RE: Sprinklers in office closets

Furniture.Thanks

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, March 16, 2007 10:30 AM
To: [email protected]
Subject: RE: Sprinklers in office closets

Are these stud-wall closets, or furniture?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thomas
Reinhardt
Sent: Friday, March 16, 2007 11:27 AM
To: [email protected]
Subject: Sprinklers in office closets

Hi Guys,



I recently did an inspection of a sprinklered building. In the office
setting the business has installed closets for each work cubicle
(station).The closets are not floor to ceiling; however, each person can
store files coats etc... We've adopted NFPA 13(2002 edition). I've
looked at Chapter 8 section 8.1.1 and the annex A 8.1.1. NFPA 13 does
talk about closets but that is in residential setting. In order to
sprinkler the closets they would have to drop a feed from the branch
lines above, which is a raised open ceiling. Any help would be
appreciated. Thanks Tom



Tom Reinhardt

Wheeling Fire Inspector

Wheeling, IL

60090   Phone 1-847-459-2669



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to