Not to be mistaken with so called "furniture" that is actually building
construction. When the framers of the standard exempted furniture its
apparent that their intent was to exclude the need for sprinkler protection
of factory manufactured filing and storage cabinets, desks, credenzas and
the like. I've run across projects where a large closet that's been field
finished with birch plywood, melamine, mdf or other such materials used in
the fabrication of "furniture" are being deemed furniture and thus
attempting to employ the sprinkler exemption. 

Obviously there are provisions in the standard as to when a "closet"
requires sprinkler protection and when it does not. Lets not allow a play on
words to circumvent the technical requirements of the standard. If this is
allowed to occur we will end up with large unprotected hazards that the
standard never intended to exempt. 

Food for thought.

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis
Sent: Friday, March 16, 2007 11:38 AM
To: [email protected]
Subject: RE: Sprinklers in office closets

Furniture does not require internal sprinkler protection. 

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thomas
Reinhardt
Sent: Friday, March 16, 2007 11:31 AM
To: [email protected]
Subject: RE: Sprinklers in office closets

Furniture.Thanks

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Friday, March 16, 2007 10:30 AM
To: [email protected]
Subject: RE: Sprinklers in office closets

Are these stud-wall closets, or furniture?

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thomas
Reinhardt
Sent: Friday, March 16, 2007 11:27 AM
To: [email protected]
Subject: Sprinklers in office closets

Hi Guys,

 

I recently did an inspection of a sprinklered building. In the office
setting the business has installed closets for each work cubicle
(station).The closets are not floor to ceiling; however, each person can
store files coats etc... We've adopted NFPA 13(2002 edition). I've
looked at Chapter 8 section 8.1.1 and the annex A 8.1.1. NFPA 13 does
talk about closets but that is in residential setting. In order to
sprinkler the closets they would have to drop a feed from the branch
lines above, which is a raised open ceiling. Any help would be
appreciated. Thanks Tom

 

Tom Reinhardt

Wheeling Fire Inspector

Wheeling, IL

60090   Phone 1-847-459-2669

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to