I have not done it...but have seen institutional heads used.  They are
"hardened" and don't project too much.  I play racquetball and if you
hit the location on the wall where the sprinklers would likely
be.....you did not make a good shot.

Paul Sincaglia



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Wednesday, March 21, 2007 2:11 PM
To: [email protected]
Subject: Re: Racquetball court

Can you do sidewall sprinklers from opposite sides to give you full
coverage 
of the 20ft dim.? What is the from to back dim. of the court?
Reliable has DH56 and DH8 for 8 to 14 Ft throw and up to 28 Ft width if
your 
court is 28 lf or less front to back come from each side with one HSW
and 
your done. Available with concealed cover to help deflect balls as well
as 
any head guard. You may want to consider a WMG bell guard around the
head as 
well.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Karen Purvis" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, March 21, 2007 9:14 AM
Subject: Racquetball court


> Ok guys I need some help. I am trying to find a head that could be
used in 
> a
> racquetball court. It has to be a sidewall head because to top of the 
> court
> is the roof. The court is 20' wide which means I probably need an
extended
> coverage head. I have talked with Tyco and he had no suggestions. I
know
> these courts have been around for years so at some point someone has
> sprinkled them Any help would be great.
>
> Karen Purvis
> Designer
> Facility Systems Consultants
> Knoxville, TN 37902
> 865-246-0164
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to