What I know of 2003 IBC 1614 Exception 2. says Detached one - and two family dwellings----in seismic Categories A B or C---Where the short period spectral response is less than Ss=0.4g are exempt.

This is the only blanket ABC exempt I've seen.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Charles Thurston" <[EMAIL PROTECTED]>
To: "Cliff Whitfield" <[email protected]>
Sent: Thursday, March 22, 2007 1:06 PM
Subject: Re[2]: Seismic and building codes


Hello Cliff,

I hope they figure it out before next week as that is where I'll be
all week Intermediate design school.....  Wish me luck

Thursday, March 22, 2007, 11:37:22 AM, you wrote:

Roland,

We were taught in the intermediate design school (2005) that Category A & B
were exempt like Brian mentioned in an earlier post.  Were we taught
incorrectly or has something changed since them?

Cliff

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, March 22, 2007 11:30 AM
To: [email protected]
Subject: Re: Seismic and building codes

I don't think the CA boys know the answer since they always have to
provide seismic protection.

You have to protect ALL structures until proven otherwise is the
starting point.  Go to IBC 1614.1 for that statement AND the
exceptions when protection is not required.  We did a couple of
articles in Sprinkler Age about this matter.  Significant break
points are Design Category A and a low spectral response (Ss of 0.15g
or Sl of 0.04g)


Roland

On Mar 22, 2007, at 8:53 AM, Thom McMahon wrote:

Probably you CA guys can answer this off the tops of your heads,
but I'll take help from anywhere.

Using the IBC 2003, chapters 16 and 18, "When is seismic bracing
required?"
Here's the building info:

Assembly building over 300 occupancy
Type V construction (all wood)
a. Seismic importance factor IE = 1.25
b. Seismic Use Group = 3
c. Mapped Spectral Response acceleration (i. ss = 0.259  ii. si =
0.066
d. Site Class = B
e. Spectral Response Coefficients: (i. SDS = 0.18  ii. SDI = 0.04)
f. Seismic Design Category = B
g. Basic seismic Force Resisting System
h. Response Modification Factor(s) R=3
i. Seismic Response Coefficient(s) Cs=0.0429
j. Analysis Procedure used:
k. Seismic Base Shear:

The above is all the info given by the Arch & Structural engineer.
We've asked the building Dept. and they need to ask ICC. Our
question to them and to you all is the same.

"When do we need to provide seismic bracing on our fire sprinkler
system? At what Site Class or Seismic Design Category, or
combination, do we need to provide seismic protection?
NFPA 13, 2007 9.3 "Where water based fire protection systems are
required to be protected against damage from earthquakes, the
requirements of 9.3 shall apply, unless the requirements of 9.3.1.2
are met."

Lost in ICC Limbo!

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Roland Huggins"
<[EMAIL PROTECTED]>
To: "SprinklerFORUM" <[email protected]>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


--
Best regards,
Charles                            mailto:[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to