It gets uglier if you are in the 2003 edition of the IBC. It literal
says you can NOT use NFPA 13 for seismic design. 2003 IBC excludes
the section of ACSE 7 that allows the use of NFPA 13 and ASCE 7
requires you to proof the calculated force (can be done) and
displacement (here's the rub) is greater with 13. I did an article
in the NFPA Journal in this issue. See:
http://www.firesprinkler.org/techservices/articles/nfpa0501seismic.pdf
After the TIA on 2002, the latest ASCE 7 now embraces 13.
Roland
On Mar 22, 2007, at 1:34 PM, Brooks, Bill wrote:
This answer is based on the 2003 IBC, and I've posted it previously
here.
It looks like the answer is in your list where the Seismic Design
Category
is listed as B. The code text and the referenced ASCE 7 has been
rearranged
somewhat in the 2006 IBC.
My previous response follows:
In case you don't want to read all the way down to the bottom, the
"answer"
is:
1. Step 1 - Architect identifies Building Classification
2. Step 2 - Structural engineer identifies Seismic Design Category
3. Step 3 - If both parties above do their jobs correctly, bracing
is not
necessary for Seismic Design Categories A and B.
The sprinkler designer should NEVER attempt to perform Steps 1 and 2.
You might also note the reference to storage racks. You don't want
to get
into a situation where you are bracing your rack sprinkler system
using
non-braced racks as your support points.
Now the longer explanation:
The difficulty with determining when bracing is required is
compounded by
the fact that the information comes from two documents (IBC 2003
and ASCE
7-02) and that there are multiple factors, use groups, etc, that
must be
defined. The need for bracing cannot be determined solely by the
sprinkler
designer. The project architect and structural engineer must play
a role.
In some cases you could have an MEP engineering firm create a spec
that is
in conflict with the architect's and structural engineer's
determinations.
These are the steps required to determine if seismic bracing is
necessary
for a sprinkler system:
1. Determine Building Classification (I, II, III, or IV) to
identify its
Seismic Importance Factor. To do this refer to IBC 2003, Table
1604.5. The
values are between 1.00 and 1.50.
THE SPRINKLER DESIGNER CAN MAKE A GUESS AT THIS ONE, BUT THE PROJECT
ARCHITECT WOULD BE THE RESPONSIBLE INDIVIDUAL TO MAKE THE BUILDING
CLASSIFICATION DETERMINATION
2. Look at Table 1604.5 footnote a to determine the Seismic Use
Group.
ONCE THE BUILDING CLASSIFICATION IS IDENTIFIED, THE PROJECT
ARCHITECT WOULD
PASS THIS INFORMATION ON TO THE STRUCTURAL ENGINEER. THE STRUCTURAL
ENGINEER USES THE SEISMIC USE GROUP IN CONJUNCTION WITH STEP 3 BELOW.
3. Determine Seismic Design Category based on ground motion using
Tables
1616.3(1) and 1616.3(2). Note ground motion factors on left and
Seismic Use
Group on top.
THE STRUCTURAL ENGINEER MUST EVALUATE THE GROUND MOTION VALUES AND
DETERMINE
THE SEISMIC DESIGN CATEGORY
4. Determine need for seismic bracing using ASCE 7-02. 9.6.1
establishes
the need for bracing of Architectural, Mechanical, and Electrical
Components
and Systems. There are 6 exceptions to this paragraph, and these
exceptions
are related to the Seismic Design Category determined above. In
order to
come up with the "answer" one other piece of information is
needed. This is
the Component Importance Factor from ASCE 7-02, 9.6.1.5. Quoting:
"9.6.1.5 Component Importance Factor. The component importance
factor (Ip)
shall be selected as follows:
Ip = 1.5 life safety component required to function after an
earthquake
(e.g. fire protection sprinkler system)
Ip = 1.5 component that contains hazardous content
Ip = 1.5 storage racks in structures open to the public (e.g.,
warehouse
retails stores)
Ip = 1.0 all other components
In addition, for structures in Seismic Use Group III:
Ip = 1.5 all components needed for continued operation of the
facility or
whose failure could impair the continued operation of the facility"
Once the Component Importance Factor is identified, the 6
exceptions to
9.6.1 can be reviewed to determine the need for seismic bracing. Only
exceptions 1, 2, and 4 are applicable to the sprinkler system:
"Exception: The following components are exempt from the
requirements of
this Section:
1. All components in Seismic Design Category A
3. Mechanical and electrical components in Seismic Design Category B.
4. Mechanical and electrical components in structures assigned to
Seismic
Design Category C provided the (component) importance factor Ip is
equal to
1.0."
HERE IS WHERE THE ANSWER COMES IN. DURING THE DESIGN PROCESS THE
ARCHITECT
DETERMINES THE BUILDING CLASSIFICATION AND PASSES THIS INFORMATION
ON TO THE
STRUCTURAL ENGINEER. THE STRUCTURAL ENGINEER DETERMINES GROUND MOTION
FACTORS AND IDENTIFIES THE SEISMIC DESIGN CATEGORY. THEN, THE
SPRINKLER
CONTRACTOR USES ASCE 7-02, 9.6.1 TO DETERMINE THE NEED FOR
BRACING. AS YOU
CAN SEE, THE ANSWER IS GOING TO BE YES FOR DESIGN CATEGORIES C, D,
E, AND F
BECAUSE THE SPRINKLER SYSTEM COMPONENT IMPORTANCE FACTOR IS 1.5.
THE ANSWER
WILL BE NO FOR DESIGN CATEGORIES A AND B.
Bill Brooks
412-365-3712
412-365-3350 FAX
412-400-6528 Cell
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Thom
McMahon
Sent: Thursday, March 22, 2007 11:53 AM
To: [email protected]
Subject: Re:Seismic and building codes
Probably you CA guys can answer this off the tops of your heads,
but I'll
take help from anywhere.
Using the IBC 2003, chapters 16 and 18, "When is seismic bracing
required?"
Here's the building info:
Assembly building over 300 occupancy
Type V construction (all wood)
a. Seismic importance factor IE = 1.25
b. Seismic Use Group = 3
c. Mapped Spectral Response acceleration (i. ss = 0.259 ii. si =
0.066
d. Site Class = B
e. Spectral Response Coefficients: (i. SDS = 0.18 ii. SDI = 0.04)
f. Seismic Design Category = B
g. Basic seismic Force Resisting System
h. Response Modification Factor(s) R=3
i. Seismic Response Coefficient(s) Cs=0.0429
j. Analysis Procedure used:
k. Seismic Base Shear:
The above is all the info given by the Arch & Structural engineer.
We've asked the building Dept. and they need to ask ICC. Our
question to
them and to you all is the same.
"When do we need to provide seismic bracing on our fire sprinkler
system? At
what Site Class or Seismic Design Category, or combination, do we
need to
provide seismic protection?
NFPA 13, 2007 9.3 "Where water based fire protection systems are
required to
be protected against damage from earthquakes, the requirements of
9.3 shall
apply, unless the requirements of 9.3.1.2 are met."
Lost in ICC Limbo!
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Roland Huggins" <[EMAIL PROTECTED]>
To: "SprinklerFORUM" <[email protected]>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum