Ron, I don't know about the code section but wouldn't the tank be the same as any other obstruction? We had a foam tank once (due to height) become an obstruction to sprinkler discharge so they needed to move sprinklers. It might be time for some education, if the room is provided with sprinklers and is appropriate for the space ( I would assume OH2 at least) and the tank does not create an obstruction to sprinkler discharge, have an educated discussion with the ahj
Michael O'Brian Code Savvy Consultants www.codesavvyconsultants.com ************************************************ Take a look at www.inspector911.com the first site dedicated to code enforcmenet (inspectors, fire marhsals, building officals, and plan reviewers). -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Garth W. Warren Sent: Monday, March 26, 2007 3:59 PM To: [email protected] Subject: Re: Diesel pump fuel tank protection - IFC 3404.2.7.7 Ron - I have never seen a head below the fuel tank of a fire pump. Sorry, I know that does not help much. Garth a fitter ----- Original Message ----- From: "Fletcher, Ron" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Monday, March 26, 2007 1:10 PM Subject: Diesel pump fuel tank protection - IFC 3404.2.7.7 A local AHJ is requiring a sprinkler head under a diesel fuel tank in fully sprinklered fire pump room. >From the AHJ - "IFC 3404.2.7.7 Design of supports requires compliance with NFPA #30. NFPA 30-2003, 4.3.1.3: requires that steel support structures for tanks storing Class I, Class II, or Class III liquids be protected by materials having a fire resistance rating of not less than 2-hours." The intent of IFC 3404.2.7.7 is to require protection of the tank supports regardless of capacity. NFPA #30, 4.1.1 This chapter shall apply to the following: 4.1.1(2) "The storage of flammable and combustible liquids in portable tanks and bulk containers whose capacity exceeds 3000 L (793 gal)..." AHJ contends that 4.1.1 and 4..1.(2) are not applicable because the IFC is referencing the tank supports and does not specify a minimum size. Has any one else run into the requirement for a sprinkler under the fuel tank in a fully sprinklered pump room and what did you fight or comply. Does anyone know of interpretations or commentary regarding tank supports. Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum