Ron,

I don't know about the code section but wouldn't the tank be the same as any
other obstruction?  We had a foam tank once (due to height) become an
obstruction to sprinkler discharge so they needed to move sprinklers.  It
might be time for some education, if the room is provided with sprinklers
and is appropriate for the space ( I would assume OH2 at least) and the tank
does not create an obstruction to sprinkler discharge, have an educated
discussion with the ahj

Michael O'Brian
Code Savvy Consultants
www.codesavvyconsultants.com

************************************************
Take a look at www.inspector911.com the first site dedicated to code
enforcmenet (inspectors, fire marhsals, building officals, and plan
reviewers).  
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: Monday, March 26, 2007 3:59 PM
To: [email protected]
Subject: Re: Diesel pump fuel tank protection - IFC 3404.2.7.7

Ron - I have never seen a head below the fuel tank of a fire pump.  Sorry, I
know that does not help much.

Garth
a fitter
----- Original Message ----- 
From: "Fletcher, Ron" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, March 26, 2007 1:10 PM
Subject: Diesel pump fuel tank protection - IFC 3404.2.7.7


A local AHJ is requiring a sprinkler head under a diesel fuel tank in
fully sprinklered fire pump room.

>From the AHJ - "IFC 3404.2.7.7 Design of supports requires compliance
with NFPA #30.
NFPA 30-2003, 4.3.1.3: requires that steel support structures for tanks
storing Class I, Class II, or Class III liquids be protected by
materials having a fire resistance rating of not less than 2-hours." The
intent of IFC 3404.2.7.7 is to require protection of the tank supports
regardless of capacity.

NFPA #30, 4.1.1 This chapter shall apply to the following:
4.1.1(2) "The storage of flammable and combustible liquids in portable
tanks and bulk containers whose capacity exceeds 3000 L (793 gal)..."

AHJ contends that 4.1.1 and 4..1.(2) are not applicable because the IFC
is referencing the tank supports and does not specify a minimum size.

Has any one else run into the requirement for a sprinkler under the fuel
tank in a fully sprinklered pump room and what did you fight or comply.
Does anyone know of interpretations or commentary regarding tank
supports.

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to