Todd,
Thanks for the info, I appreciate the help.

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- work
Sent: Tuesday, March 27, 2007 11:10 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System

Brian,

First off, welcome to the club.

Secondly, does this mercantile space have a drop ceiling? If so, that 
may dictate your spacing somewhat, especially if they want center of tile.

Overages can be tricky; it depends a lot on the building 
configuration, location of rooms, etc. A set of plans came across my 
desk yesterday with a 0.15/900 demand, which would equate to a base 
of 135 gpm. The demand flow in the sprinkler system is 229 gpm, 
almost a 70% overage. It was completely appropriate based on the 
configuration. If I need to estimate the water demand, what I like to 
do is lay out the sprinklers first, using the ceiling plan and the 
NFPA standards. From there I would locate the remote area, count the 
number of sprinklers in that area and multiply it by the minimum 
flow. I would assign the overage from that figure; typically 10% for 
grids and 25% for trees. (In the example I cited above, there were 12 
sprinklers at a flow of 18 gpm per sprinkler, or a total of 216 gpm. 
Therefore the actual flow of 229 gpm was only a 6% overage. My 
estimate would have been 216 x 1.25 = 270 gpm.)

It's not an exact science, so accept it as that. I hope this helps.

Todd





>Let me start by saying I've only been in the sprinkler world for just
>over a
>year so if any thing I ask is "rookie-ish" please keep that in mind. I'm
>looking for ideas that some of you may use when starting a new project
>when
>it comes to selecting what heads (head spacing) to use. For example: I
>am
>starting a retail store (mercantile) that has a Static of 47 psi
>Residual of
>42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is
>take the density x area of operation x 1.4 (for overage) + hose
>allowance.
>That gets me roughly the system gpm demand.  So .20 x 1500 = 300 x 1.4 =
>420
>+ 250 (hose) = 670 gpm.  I then plot that gpm on my water supply curve
>(N1.85) to get the psi for that gpm; in this case that's around 45psi.
>From
>that psi I take out for the BFP, elevation, 40% (friction loss & etc)
>and
>whatever is left I find a head with an end head pressure that's slightly
>under that and away I go.... Any thoughts? Suggestions? Better Ideas?
>
>
>
>            Regards,
>
>               Brian Harris
>First Defense Fire Protection
>

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to